In: Electrical Engineering
I'm working on a project where I need to design a transmission line tap for a station generator. The parameters include sizing three switches for the tap where at least one is a loop break switch. From where to start? What kind of calculations are needed to size the switches? What are those switches?
7. Calculate Operating Conditions of the Motors
If the motors are operating at 12 kV, this represents 12 kV/13.8 kV
= 0.87 per-unit voltage. At unity power factor, the load is given
as three-quarters or 0.75 p.u.
Thus, expressed in per unit, the combined motor current is
obtained by using the equation:
Iper unit = per-unit power/per-unit voltage = 0.75/0.87 = 0.862 ?0°
p.u.
8. Calculate the Generator Terminal Voltage
The voltage at the generator terminals is:
VG = Vmotor + the voltage drop through transformers and
transmission line
VG = 0.87?0° + 0.862 ?0°(j0.101 + j0.313 + j0.101)
VG = 0.87 + j0.444 = 0.977 ?27.03° p.u.
In order to obtain the actual voltage, multiply the per-unit
voltage by the base voltage at the generator. Thus,
VG = (0.977 ?27.03°) (13.8 kV) = 13.48 ?27.03° kV
Single line diagram
This technical article explains how to calculate and draw a single
line diagram of the three-phase, 60-Hz system power system with
generators, motors, transformers and lines. The following
components comprise a simplified version of a power system, listed
in sequential physical order from the generator location to the
load:
Two steam-electric generators, each at 13.2 kV
Two step-up transformers, 13.2/66 kV
Sending-end, high-voltage bus at 66 kV
One long transmission line at 66 kV
Receiving-end bus at 66 kV
A second 66 kV transmission line with a center-tap bus
Step-down transformer at receiving-end bus, 66/12 kV, supplying
four 12 kV motors in parallel and
A step-down transformer, 66/7.2 kV, off the center-tap bus,
supplying a 7.2 kV motor
Calculation Procedure
1. Identify the Appropriate Symbols
2. Draw the Required
System
The system described in the problem is shown in Figure 2. The oil
circuit breakers are added at the appropriate points for proper
isolation of equipment.
Related Calculations
It is the general procedure to use single line diagrams for
representing three-phase systems. When analysis is done using
symmetrical components, different diagrams may be drawn that will
represent the electric circuitry for positive, negative, and
zero-sequence components.
Additionally, it is often necessary to identify the grounding
connection, or whether the device is wye- or delta-connected.
This type of notation is shown in Figure 3.
Per-unit method of solving of 3-phase problems
For the system shown in Figure 4, draw the electric circuit or
reactance diagram, with all reactances marked in per-unit (p.u.)
values, and find the generator terminal voltage assuming both
motors operating at 12 kV, three-quarters load, and unity power
factor.
Generator Transformers
(each) Motor A Motor B Transmission
Line
13.8kV 25,000 kVA 15,000 kVA 10,000 kVA –
25,000 kVA 3-phase 13.2/69 kV 13.0 kV 13.0 kV –
X” = 15 percent XL = 15 percent X” = 15 percent X” = 15 percent X =
65 ?
Calculation Procedure in 8 steps
1. Establish Base Voltage through the System
By observation of the magnitude of the components in the system, a
base value of apparent power S is chosen. It should be of the
general magnitude of the components, and the choice is arbitrary.
In this problem, 25,000 kVA is chosen as the base S, and
simultaneously, at the generator end 13.8 kV is selected as a base
voltage Vbase.
The base voltage of the transmission line is then determined by
the turns ratio of the connecting transformer:
(13.8 kV)(69 kV / 13.2 kV) = 72.136 kV
The base voltage of the motors is determined likewise but with the
72.136 kV value, thus:
(72.136 kV)(13.2 kV / 69 kV) = 13.8 kV
The selected base S value remains constant throughout the system, but the base voltage is 13.8 kV at the generator and at the motors, and 72.136 kV on the transmission line.
2. Calculate the Generator Reactance
No calculation is necessary for correcting the value of the
generator reactance because it is given as 0.15 p.u. (15 percent),
based on 25,000 kVA and 13.8 kV. If a different S base were used in
this problem, then a correction would be necessary as shown for the
transmission line, electric motors, and power transformers.
3. Calculate the Transformer Reactance
It is necessary to make a correction when the transformer nameplate
reactance is used because the calculated operation is at a
different voltage, 13.8 kV / 72.136 kV instead of 13.2 kV / 69
kV.
Use the equation for correction: per-unit reactance:
(nameplate per-unit reactance) (base kVA/nameplate kVA) (nameplate
kV/base kV)2 =
(0.11) (25,000/25,000) (13.2/13.8)2 = 0.101 p.u.
This applies to each transformer.
4. Calculate the Transmission-Line Reactance
Use the equation:
Xper unit = (ohms reactance)(base kVA)/(1000)(base kV)2 =
Xper unit = (65) (25,000)/(1000)(72.1)2 = 0.313 p.u.
5. Calculate the Reactance of the Motors
Corrections need to be made in the nameplate ratings of both motors
because of differences of ratings in kVA and kV as compared with
those selected for calculations in this problem. Use the correcting
equation from Step 3, above.
For motor A:
X”A = (0.15 p.u.) (25,000 kVA / 15,000 kVA) (13.0 kV / 13.8 kV)2 =
0.222 p.u.
For motor B:
X”B = (0.15 p.u.)(25,000 kVA /10,000 kVA)(13.0 kV / 13.8 kV)2 =
0.333 p.u.
6. Draw the Reactance Diagram
The completed reactance diagram is shown in Figure 5: