Question

In: Electrical Engineering

A company plans to purchase a transformer that will be used 12 hours at full load...

A company plans to purchase a transformer that will be used 12 hours at full load and 12 hours with no load but still connected to the power supply at all times. The transformer has copper losses of 5 kW and core losses of 3.5 kW. Electricity costs $0.07/kW-hr. What is the total cost of transformer losses over a period of 1 year?

Solutions

Expert Solution

When the transformer is at full load both copper loss and core loss occur. But core loss is negligible compared to the copper loss as there will be a huge surge of current passing through it as it is in short circuit Thus total power is 5 = 8.5kW.

When the transformer is not connected to the load but is still connected to the power supply it experiences core loss mainly as the primary current loading is very small and we neglect it.Thus total power is 3.5kW.

(For reason scroll further below)

That means on a day total power loss is (12*5) + (12*3.5) = 102kW-hr/day.

It costs 0.07*102 = $7.14/day.

For a year it would cost 7.14*365 = $2606.1

Copper loss occurs when current passes through the conductor of the transformer winding and energy is dissipated as heat. It is also known as I2R loss.It is the same loss that occurs when we connect a battery to a resistor and current flows through it. The energy of the battery is dissipated as heat in the resistor. Another familiar example I can provide is the case of a light bulb, which converts the electrical energy into light and heat.

Core loss occurs due to the changing magnetic field which is dissipated in the core of the transformer.

It is categorized into three categories:

1. Hysteresis loss: To understand this best, look into the B field vs H field graph of a magnetic material which forms a close loop. The process is irreversible and there is energy loss. This occurs when the magnetic field through the core changes, the magnetization of the core material changes by expansion and contraction of the tiny magnetic domains it is composed of, due to movement of the domain walls. This process causes losses because the domain walls get snagged on defects in the crystal structure and then snap past them, dissipating energy as heat.

2. Eddy current: The changing magnetic field induces circulating currents in the core which is proportional to the area of the core. This is due to electromagnetic induction. The circular loop flows perpendicular to the magnetic field and the energy is dissipated as heat. This is the reason why we see cores made thin with insulating coatings.

3. Anamalous loss: It includes any loss other than the above two

Please leave a thumbs up if you liked my explanation.


Related Solutions

A company plans to purchase a transformer that will be used 12 hours at full load...
A company plans to purchase a transformer that will be used 12 hours at full load and 12 hours with no load but still connected to the power supply at all times. The transformer has copper losses of 5 kW and core losses of 3.5 kW. Electricity costs $0.07/kW-hr. What is the total cost of transformer losses over a period of 1 year?
1) A 25 kVA transformer supplies a load of 12 kW at power factor of 0.6...
1) A 25 kVA transformer supplies a load of 12 kW at power factor of 0.6 lagging. How much kVA can be added before the transformer is at rated load a)when the added load is at 1.0 pf? b)when the added load is at 0.866 pf leading?
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8...
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8 power factor, and 99.13% with half-rated current at unity power factor. calculate: (a) The iron loss. (b) the full-load copper loss. (c) the efficiency at 3/4 load, 0.9 power factor
An Uncontrolled Full-Wave full-bridge rectifier with RL-Source load and Discontinuous load current is to be designed...
An Uncontrolled Full-Wave full-bridge rectifier with RL-Source load and Discontinuous load current is to be designed based on the following assumptions and constraints. Design the circuit and calculate the parameters of the rectifier based on the following assumptions and constraints. Simulate the designed rectifier in PsPice and compare the simulated and the calculated results. a) The AC source is 220 V rms at 50 Hz. Vdc= 65 V, power absorbed by the resistor is 360 W. b) The AC source...
How is it possible for a (Buck-Boost) Transformer to operate a KVA load many times larger...
How is it possible for a (Buck-Boost) Transformer to operate a KVA load many times larger than the transformers KVA rating?
When a P = 720 W ideal (lossless) transformer is operated at full power with an...
When a P = 720 W ideal (lossless) transformer is operated at full power with an rms input current of I1 = 3.1 A, it produces an rms output voltage of V2 = 9.4 V. Part A) What is the input voltage, in volts? Part B) What is the output current, in amperes? Part C) Calculate the ratio of primary to secondary turns. Part D) Is this a step-up or a step-down transformer?
Spherical Manufacturing recently spent $ 12$12 million to purchase some equipment used in the manufacture of...
Spherical Manufacturing recently spent $ 12$12 million to purchase some equipment used in the manufacture of disk drives. This equipment has a CCA rate of 45 %45% and​ Spherical's marginal corporate tax rate is 35 %35%. a. What are the annual CCA deductions associated with this equipment for the first five​ years? b. What are the annual CCA tax shields for the first five​ years? c. What is the present value of the first five CCA tax shields if the...
A three phase transformer of 400kVA, 10kV/400V, Dy11 is connected to its nominal load with cosφ...
A three phase transformer of 400kVA, 10kV/400V, Dy11 is connected to its nominal load with cosφ = 1. a) Calculate the nominal primary and secondary line current. b) Calculate the corresponding currents in the primary and secondary winding. At an open circuit test, the primary line current is 0,52A with cosφ = 0,05 at nominal line voltage. The short circuit test (at nominal current) shows 214V primary line voltage and P=1,333kW per phase. c) Calculate the total iron losses and...
A company plans to purchase a new machine. There are two choices. The following are the...
A company plans to purchase a new machine. There are two choices. The following are the cash flows from two machines:        Machine A:    The machine’s initial purchase price is $99,718, and it has a singlemaintenance fee of $6,000 at the end of year 4. The machine would last for 7 years. Assume that the discount rate is 8% for this machine.      Machine B:    The machine’s initial purchase price is $10,000, and it has annualmaintenance cost of $10,000 at the end of each...
A company manager plans to purchase a machine. The company requires a high quality machine. The...
A company manager plans to purchase a machine. The company requires a high quality machine. The manager is currently considering two companies that supply this machine. The machine from company A can produce approximately 1050 units in average per day, but the standard deviation of this machine is about 250 units per day; while the machine from company B can produce approximately 900 units in average per day, but the standard deviation of this machine is about 100 units per...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT