Question

In: Physics

Copper and aluminum are being considered for a high-voltage transmission line that must carry a current...

Copper and aluminum are being considered for a high-voltage transmission line that must carry a current of 60 A. The resistance per unit length is to be 0.170 Ω/ km. Compute for each choice of cable material the current density. The current density for copper?

The current density for aluminum?

Compute the mass per meter of the cable for each material. The densities of the copper and aluminum are 8960 and 2700 kg/ m3, respectively. The mass per meter of the copper cable?

The mass per meter of the aluminum cable?

Solutions

Expert Solution

current density for copper =   (60 * 0.170 * 10-3)/(1.68 * 10-8)

                                            = 6.071 * 105 A/m2

current density for aluminium =   (60 * 0.170 * 10-3)/(2.65 * 10-8)

                                            = 3.849 * 105 A/m2

mass per meter of the copper   =   8960 * (1.68 * 10-8)/(0.170 * 10-3)

                                                  = 0.8854 kg/m

mass per meter of the aluminium =   2700 * (2.65 * 10-8)/(0.170 * 10-3)

                                                  = 0.421 kg/m


Related Solutions

A high voltage power line carries a current of 105 A at a location where the...
A high voltage power line carries a current of 105 A at a location where the Earth's magnetic field has a magnitude of 0.588 G and points the to the North, 74.7 degrees below the horizontal. Calculate the magnitude of the magnetic force exerted on a 253 m length of wire if the current in the wire flows horizontally toward the east? _____________________________________________________________ Calculate the magnitue of the magnetic force exerted on a 253 m length of wire if the...
A high-voltage power line carries a current of 122 A at a location where the Earth's...
A high-voltage power line carries a current of 122 A at a location where the Earth's magnetic field has a magnitude of 0.59 G and points to the north, 68 ∘ below the horizontal. Find the direction of the magnetic force exerted on a 330 mm length of wire if the current in the wire flows horizontally toward the east. A:force points toward north, 22 ∘∘ above the horizontal B:force points toward north, 68 ∘∘ above the horizontal C:force points...
What types of consideration must be made when selecting the appropriate type and style of conductor for high voltage and long distance transmission?
  1) What types of consideration must be made when selecting the appropriate type and style of conductor for high voltage and long distance transmission? How do thermal reaction and stress/strain propeties factor into these decision. 2) How do we acquire the metals that we used for conducting paths in our circuit? what are some impacts of these method on environment and social level?
Will a copper wire or an aluminum wire give the larger current to weight ratio for...
Will a copper wire or an aluminum wire give the larger current to weight ratio for high voltage transmission lines if both wires are to have the same resistance between any two points?
3. Electric power is transferred at very high voltages over long distances. Transmission of high voltage...
3. Electric power is transferred at very high voltages over long distances. Transmission of high voltage Explain how it reduces power loss on the lines. 4. If two points have the same potential, this test load will be taken from one point to another. Does it mean that no work will be carried out during the course? This need no force application shows that it is not? Discuss.
1. A sinusoidal voltage wave on a transmission line has real amplitude, V_0. The wave is...
1. A sinusoidal voltage wave on a transmission line has real amplitude, V_0. The wave is expressed in phasor form as V_s(z) = V_0*e^(-alpha*z)*e^(-j*(beta)*z) a. In which direction does this wave propagate and why? b. Express the given wave in real instantaneous form. c. The parameters of the line, operating at ω= 6.0×10^8 rad/s are L = 0.350 μH/m, C = 40.0 pF/m, G = 0 and R = 15.0 Ω/m. Find α,β,λ, andZ_0 (in magnitude and phase). d. Calculate...
Alternative A and Alternative B are being considered for recovering aluminum from garbage. Alternative A –...
Alternative A and Alternative B are being considered for recovering aluminum from garbage. Alternative A – has a capital cost of $100,000, a first year maintenance cost of $15,000, with maintenance increasing by $500 per year for each year after the first. Alternative B - has a capital cost of $120,000, a first year maintenance cost of $17,000, with maintenance increasing by $1,000 per year after the first. Revenues from the sale of aluminum are $20,000 in the first year,...
A copper transmission cable 100 km long and 10.0 cm in diameter carries a current of...
A copper transmission cable 100 km long and 10.0 cm in diameter carries a current of 125 A.  The copper resistivity is1.72 × 10-8 Ω.m. (a)  What is the potential drop across the cable?   (b) How much electrical energy is dissipated as thermal energy per hour?   (c) What temperature increase is required to increase the cable resistance by 5.00% ? [Thermal resistivity coefficient of copper at 25 deg C is 0.00393 (°C)-1]
When a voltage difference is applied to a piece of copper wire, a 5.0 mA current flows.
When a voltage difference is applied to a piece of copper wire, a 5.0 mA current flows. If the copper wire is replaced with a silver wire with twice the diameter of the copper wire, how much current will flow through the silver wire? The lengths of both wires are the same, and the voltage difference remains unchanged. (The resistivity of copper is 1.68 × 10-8 Ω·m, and the resistivity of silver is 1.59 × 10-8 Ω ·m)a. 1.3 mAb. 19 mAc....
Q4. A copper transmission cable 100 km long and 10.0 cm in diameter carries a current...
Q4. A copper transmission cable 100 km long and 10.0 cm in diameter carries a current of 125 A. The copper resistivity is 1.72 × 10-8 Ω.m. (a) What is the potential drop across the cable? (b) How much electrical energy is dissipated as thermal energy per hour? (c) What temperature increase is required to increase the cable resistance by 5.00% ? [Thermal resistivity coefficient of copper at 25 deg C is 0.00393 (°C)-1]
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT