Air enters an air-conditioning system that uses refrigerant-134a at 30°C and 70 percent relative humidity at a rate of 4 m3/min. The refrigerant enters the cooling section at 700 kPa with a quality of 20 percent and leaves as saturated vapor. The air is cooled to 20°C at a pressure of 90kPa .
Determine the rate of dehumidification m˙w= kg/min (Round to five decimal places)
Determine the rate of heat transfer Q˙out= kJ/min (Round to two decimal places)
Determine the mass flow rate of the refrigerant m˙R= kg/min (Round to three decimal places)
Some important assumptions to make while solving this problem are as follows
From the pH chart for R 134a and the psychrometric chart at 90 kPa (988.5 m altitude), we can get a lot of vital information required to solve this problem from the data provided in the question. Please note that due to copyright and legal issues I am not allowed to post such charts directly from the internet. However, you can easily cross-verify from any random chart available.
Chart used | Data used | Data obtained | Value |
R 134a pH chart | Saturation pressure 0.7 MPa, 0.2 quality | Enthalpy at inlet refrigerant h(ri) kJ/kg | 265 |
R 134a pH chart | Saturation pressure 0.7 MPa, saturated vapour | Enthalpy at outlet refrigerant h(ro) kJ/kg | 410 |
psychrometric chart | 30 DBT, 70% RH | Enthalpy of air inlet h(ai) kJ/kg | 84.46 |
psychrometric chart | 30 DBT, 70% RH |
The specific volume of air inlet v m3/kg |
1 |
psychrometric chart | 30 DBT, 70% RH | The absolute humidity of air inlet w(1) kg/kg | 0.02118 |
psychrometric chart | 20 DBT, 100% RH | Enthalpy of air outlet h(ao) kJ/kg | 62.19 |
psychrometric chart | 20 DBT, 100% RH | The absolute humidity of air outlet w(2) kg/kg | 0.01659 |
Given the volume flow rate of air is V = 4 m3/min
PART A
The rate of dehumidification is the change in absolute humidity
for the total mass flow rate of air. Thus it is given by
PART B
The rate of heat transfer is the total heat rejected by the air. This is obtained by multiplying the mass flow rate of air with the change in enthalpy.
PART C
The mass flow rate of the refrigerant can new obtained by balancing the heat exchange between the air and refrigerant. Thus
ANSWERS
*A humble request* - If you have any doubt, please use the comment section to communicate. Please be a little patient, it is an honest promise I will reply as soon as possible. This will clarify your doubt, and also help me to get better at answering your next questions. At the same time, If my answer helped you, please consider leaving an upvote. I hope you understand my viewpoint. Thank you :)