Question

In: Mechanical Engineering

refrigerant 134a enters the evaporator of a refrigeration system operating at steady state at -12°C and...

refrigerant 134a enters the evaporator of a refrigeration system operating at steady state at -12°C and a quality of 20% at a velocity of 7 m/s. At the exit, the refrigerant is a saturated vapor at -12°C. The evaporator flow channel has constant diameter of 1.7cm.

Determine the mass flow rate of the refrigerant in kg/s

Determine the velocity at the exit in m/s

Solutions

Expert Solution


Related Solutions

Refrigerant 134a enters the evaporator of a refrigeration system operating at steady state at -4oC and...
Refrigerant 134a enters the evaporator of a refrigeration system operating at steady state at -4oC and a quality of 20% at a velocity of 6 m/s. At the exit, the refrigerant is a saturated vapor at -4oC. The evaporator flow channel has constant diameter of 1.7 cm. Determine the mass flow rate of the refrigerant, in kg/s, and the velocity at the exit, in m/s.
Refrigerant 134a enters a horizontal pipe operating at steady state at 40°C, 300 kPa, and a...
Refrigerant 134a enters a horizontal pipe operating at steady state at 40°C, 300 kPa, and a velocity of 25 m/s. At the exit, the temperature is 70°C and the pressure is 240 kPa. The pipe diameter is 0.01 m. Determine: (a) the mass flow rate of the refrigerant, in kg/s, (b) the velocity at the exit, in m/s, and (c) the rate of heat transfer between the pipe and its surroundings, in kW.
Refrigerant 134a enters an insulated compressor operating at steady state as saturated vapor at -26oC with...
Refrigerant 134a enters an insulated compressor operating at steady state as saturated vapor at -26oC with a volumetric flow rate of 0.18 m3/s. Refrigerant exits at 8 bar, 70oC. Changes in kinetic and potential energy from inlet to exit can be ignored. Determine the volumetric flow rate at the exit, in m3/s, and the compressor power, in kW.
Refrigerant 134a enters an insulated compressor operating at steady state as saturated vapor at -20oC with...
Refrigerant 134a enters an insulated compressor operating at steady state as saturated vapor at -20oC with a volumetric flow rate of 0.18 m3/s. Refrigerant exits at 9 bar, 70oC. Changes in kinetic and potential energy from inlet to exit can be ignored. Determine the volumetric flow rate at the exit, in m3/s, and the compressor power, in kW.
Problem 4.016 SI Refrigerant 134a enters a horizontal pipe operating at steady state at 40°C, 300...
Problem 4.016 SI Refrigerant 134a enters a horizontal pipe operating at steady state at 40°C, 300 kPa, and a velocity of 25 m/s. At the exit, the temperature is 90°C and the pressure is 240 kPa. The pipe diameter is 0.1 m. Determine: (a) the mass flow rate of the refrigerant, in kg/s, (b) the velocity at the exit, in m/s, and (c) the rate of heat transfer between the pipe and its surroundings, in kW.
A vapor-compression refrigeration cycle operates at steady state with Refrigerant 134a as the working fluid. Saturated...
A vapor-compression refrigeration cycle operates at steady state with Refrigerant 134a as the working fluid. Saturated vapor enters the compressor at 2 bar, and saturated liquid exits the condenser at 10 bar. The isentropic compressor efficiency is 80%. The mass flow rate of refrigerant is 7 kg/min. Determine: (a) the compressor power, in kW. (b) the refrigeration capacity, in tons. (c) the coefficient of performance.
Refrigerant 134a at p1 = 30 lbf/in2, T1 = 40oF enters a compressor operating at steady...
Refrigerant 134a at p1 = 30 lbf/in2, T1 = 40oF enters a compressor operating at steady state with a mass flow rate of 400 lb/h and exits as saturated vapor at p2 = 160 lbf/in2. Heat transfer occurs from the compressor to its surroundings, which are at T0 = 40oF. Changes in kinetic and potential energy can be ignored. The power input to the compressor is 4 hp.   Determine the heat transfer rate for the compressor, in Btu/hr, and the...
Refrigerant 134a enters an air conditioner compressor at 4 bar, 20°C, and is compressed at steady...
Refrigerant 134a enters an air conditioner compressor at 4 bar, 20°C, and is compressed at steady state to 12 bar, 80°C. The volumetric flow rate of the refrigerant entering is 7.5 m3/min. The work input to the compressor is 112.5 kJ per kg of refrigerant flowing. Neglecting kinetic and potential energy effects, determine the magnitude of the heat transfer rate from the compressor, in kW.
A steady-flow Carnot refrigeration cycle uses refrigerant-134a as the working fluid. The refrigerant changes from saturated...
A steady-flow Carnot refrigeration cycle uses refrigerant-134a as the working fluid. The refrigerant changes from saturated vapor to saturated liquid at 40 C in the condenser as it rejects heat. The evaporator pressure is 120 kPa. Determine: (a) the amount of heat absorbed from the refrigerated space; qL = _______________ kJ/kg (b) the net work input; and wnet = ______________ kJ/kg (c) the coefficient of performance of the system. COP = _____________
Refrigerant R-134a enters the compressor of a refrigeration machine at 140 kPa pressure and -10 °...
Refrigerant R-134a enters the compressor of a refrigeration machine at 140 kPa pressure and -10 ° C temperature and exits at 1 MPa pressure. The volumetric flow of the refrigerant entering the compressor is 0.23 m3 / minute. The refrigerant enters the throttling valve at 0.95 MPa pressure and 30 ° C, exiting the evaporator as saturated steam at -18 ° C. The adiabatic efficiency of the compressor is 78%. Show the cycle in the T-s diagram. In addition, a)...