Question

In: Electrical Engineering

A three phase source supplies a building with 18 KV which has a group of four...

A three phase source supplies a building with 18 KV which has a group of four 3-phase loads as follows:

LOAD 1: Wye connected; S=444 KVA and 0.84 lagging power factor

LOAD 2: Delta connected; S=693.75 KVA and 0.64 leading power factor

LOAD 3: Wye connected; Z= 140 + j240 Ω

LOAD 4: Unbalanced wye-connected and grounded load, with  Za = 14+j3 Ω , Zb = 5-j24Ω and Zc =1+j14 Ω

What is the current phasor flowing through each conductor?

Solutions

Expert Solution


Related Solutions

An unbalanced three-phase wye-connected and grounded load is connected to a balanced three-phase four-wire source. The...
An unbalanced three-phase wye-connected and grounded load is connected to a balanced three-phase four-wire source. The load impedances are Za = 14+j3 Ω , Zb = 5-j24Ω and Zc =1+j14 Ω  and the phase a line voltage has an effective value of 18 Kv: use line-to-neutral voltage of phase A as a reference. Find the line and neutral current, also find the reactive power delivered to load and power factor.
Plate values of a three-phase transformer are given below: 1600 kVA, 15 kV / 0,4 kV,...
Plate values of a three-phase transformer are given below: 1600 kVA, 15 kV / 0,4 kV, 50 Hz, i0 = 1.2%; ukN= 6%, idle losses 2450 W, rated power copper losses 14500 W; Dy5 connected.. III) If there is 75% load in the power factor with 0.85 inductance and 0.85 capacity. At what times of the day can capacity loading be seen? What solution should be applied to prevent voltage change? IV) Draw the fastening group. How can this transformer...
Plate values of a three-phase transformer are given below: 1600 kVA, 15 kV / 0,4 kV,...
Plate values of a three-phase transformer are given below: 1600 kVA, 15 kV / 0,4 kV, 50 Hz, i0 = 1.2%; ukN= 6%, idle losses 2450 W, rated power copper losses 14500 W; Dy5 connected.. Calculate the secondary VOLTAGE separately at 75% load in the power factor with 0.85 inductance and 0.85 capacity. Compare and interpret the results. At what times of the day can capacity loading be seen? What solution should be applied to prevent voltage change?
A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has...
A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has reactance of 1.65 pu. The generator is operated on an infinite bus of 15 kV voltage and delivers 100 MVA at 0.8 Power Factor, lagging. a)Determine the internal voltage (E_i), the power angle (δ), and the line current of the machine. b)If the field current of the machine is reduced by 10%, while the mechanical power input to the machine is maintained constant, determine...
2) A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and...
2) A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has reactance of 1.65 pu. The generator is operated on an infinite bus of 15 kV voltage and delivers 100 MVA at 0.8 Power Factor, lagging. a)Determine the internal voltage (E_i), the power angle (δ), and the line current of the machine. b)If the field current of the machine is reduced by 10%, while the mechanical power input to the machine is maintained constant,...
For 345 KV, a three conductor per phase are to be used at 0.30 meters per...
For 345 KV, a three conductor per phase are to be used at 0.30 meters per conductor in a flat horizontal layout. The distance between the centers of each bundle is 4 meters in a delta configuration. GMR for the conductors is 0.012 m Find: GMD, L, and XL
A three-phase positive sequence Y-connected source supplies 12 kVA with a power factor of 0.75 lagging...
A three-phase positive sequence Y-connected source supplies 12 kVA with a power factor of 0.75 lagging to a parallel combination of a Y-connected load and a Δ-connected load. The Y-connected load uses 6 kVA at a power factor of 0.6 lagging and has an a-phase current of 12∠−30∘A Part A: Find the complex power per phase of the  Δ-connected load. (VA) Part B: Find the magnitude of the voltage. (Volts)
QUESTION 2 Group A has three scores, 32, 18, 28. Group B has three scores, 12,...
QUESTION 2 Group A has three scores, 32, 18, 28. Group B has three scores, 12, 40, 39. Group C has three scores, 37, 35, 45. Calculate the F-value. Round to one digit. QUESTION 4 Group A has three scores, 11, 26, 22. Group B has three scores, 16, 28, 33. Group C has three scores, 21, 36, 25. Calculate the grand mean (round to two digits). QUESTION 5 Group A has three scores, 11, 47, 27. Group B has...
A 500-kV, 60 Hz, three-phase completely transposed overhead line has three ASCR 1113-kcmil conductors per bundle,...
A 500-kV, 60 Hz, three-phase completely transposed overhead line has three ASCR 1113-kcmil conductors per bundle, with 0.5 m between conductors in the bundle. The horizontal phase spacing between bundle centers are 10, 10, and 20 m. With a length of 190 km, the line delivers 1800 MW at 475 kV and at 0.90 power factor leading to the receiving end at full load. Using the nominal π circuit, calculate the: (a) ABCD parameters, (b) sending-end voltage and current, (c)...
A three-phase 60-Hz transmission line is energized with 420 kV at the sending end. This line...
A three-phase 60-Hz transmission line is energized with 420 kV at the sending end. This line is lossless and 400 km long with ? = 0.001265 rad/km and ?? = 260 Ω. a) Suppose a three-phase short-circuit occurs at the receiving end. Determine the receiving end current and the sending end current. b) Determine the reactance and MVar of a shunt reactor to be installed at the load bus to limit the no-load receiving-end voltage to 440 kV. c) When...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT