Question

In: Electrical Engineering

A three-phase 50Hz, 500MVA 15kV generator has an inertia constant of 2pu/s. a) For a given...

A three-phase 50Hz, 500MVA 15kV generator has an inertia constant of 2pu/s.
a) For a given power system the initial load angle is δ0 and the change in
momentum is M. Following a small disturbance the load angle increases
to δ1. If the accelerating power associated with disturbance is Pa deduce
an equation that expresses δ1 in terms of M, Pa δ0 and time, t.
b) Calculate the
i. Synchronous speed
ii. Change in momentum
c) Initially the mechanical and electrical power delivered equal 1 pu and the
load angle is 10⁰. Calculate the
i. Maximum electrical power
ii. Accelerating power
d) A fault occurs which reduces the electrical power to zero. Calculate the
i. accelerating power
ii. power load angle after 0.05s

Solutions

Expert Solution


Related Solutions

Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1...
Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1 ?. The total mechanical and stray losses are 1.5kW. The core losses are neglected. Assume that the magnetization curve of the generator is linear. If the generator operates at full load at a unity power factor, calculate the following: a.The speed of rotation of the generator at full load. b.The voltage regulation of the generator. c.The developed torque on the shaft of the generator....
A 400V, three phase, 50Hz, 4 pole induction motor is operating at a per unit slip...
A 400V, three phase, 50Hz, 4 pole induction motor is operating at a per unit slip of 40KW from the suppply. Under these conditions stator losses amount to 2.2 KW and rotational losses due to friction and windage amount to 1.4KW. Calculate the net horsepower and torque developed.
A 3 phase 50Hz overhead line has the following constants: R/phase=2ohms; Xl/phase=10ohms and Y/phase=4x10^-4 siemens. The...
A 3 phase 50Hz overhead line has the following constants: R/phase=2ohms; Xl/phase=10ohms and Y/phase=4x10^-4 siemens. The line is supplying a balanced load of 24000 KVA, 0.8 pf lagging at 66KV. Compute for the sending end voltage, sending end current and efficiency of the line using: a.Nominal T Method b.Nominal pi Method c.Rigorous Method
A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has...
A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has reactance of 1.65 pu. The generator is operated on an infinite bus of 15 kV voltage and delivers 100 MVA at 0.8 Power Factor, lagging. a)Determine the internal voltage (E_i), the power angle (δ), and the line current of the machine. b)If the field current of the machine is reduced by 10%, while the mechanical power input to the machine is maintained constant, determine...
Given a balanced three-phase delta-connected generator with positive sequence and voltage Vbc=350∠−90∘Vbc=350∠−90∘ Vrms. The generator feeds...
Given a balanced three-phase delta-connected generator with positive sequence and voltage Vbc=350∠−90∘Vbc=350∠−90∘ Vrms. The generator feeds a balanced three-phase delta-connected load having an impedance of 43.5+j27 Ω/phase. The impedance of the line connecting the generator to the load is 1.5+j1 Ω/phase.  i) Calculate the total real power consumed by the load. [5] ii) Calculate the percentage of the total available real power lost in the lines.[3]   
Diesel Generator A I MVA diesel three-phase generator is rated at 4.16 kV, 60 Hz, and...
Diesel Generator A I MVA diesel three-phase generator is rated at 4.16 kV, 60 Hz, and connected as Y its neutral is kept floating. It is directly tied to three loads, one consuming 50% of its capacity, and each of the other two consuming 25% of its capacity. A three-phase to ground fault could occur at any of the loads. Draw a one-line diagram of this system, then describe what type of faults could occur in the generator and diesel...
Explain with the diagram the structure and theory of the work of a three-phase electric generator,...
Explain with the diagram the structure and theory of the work of a three-phase electric generator, specifying the function of each part ؟؟
2) A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and...
2) A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has reactance of 1.65 pu. The generator is operated on an infinite bus of 15 kV voltage and delivers 100 MVA at 0.8 Power Factor, lagging. a)Determine the internal voltage (E_i), the power angle (δ), and the line current of the machine. b)If the field current of the machine is reduced by 10%, while the mechanical power input to the machine is maintained constant,...
A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to...
A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to a Y-connected load. The transmission line has an impedance of (0.02+j0.4) Ω/phase, and the load has an impedance of (4+j3) Ω per phase. Determine the;(a)line current (IL) at the load [2Marks] (b)line and phase voltage of the load[2 Marks](c)active power, reactive and apparent power [2 Marks](d) power factor and specify whether it is lagging or leading. [4 Marks]
for the gas phase isomerization of dimethyl maleate, the rate constant in s-1 has been determined...
for the gas phase isomerization of dimethyl maleate, the rate constant in s-1 has been determined at several temperatures. when ln k is plotted against the reciprocal of the Kelvin temperature, the resulting linear plot has a slope of -1.34 x 104 K and a y-intercept of 11.8. The value of the rate constant for the gas phase isomerization of dimethyl maleate at 683 K is _ s-1 enter your answer to one significant figure