In your opinion, what are the primary limitations to the accuracy of outdoor air-temperature sensors, and what could be done to reduce these limitations?
The Causes of calibration failure
1. Self-heating in thermistors and PRTs
When thermistors and PRTs are calibrated, a nominal excitation current is applied. The amount of current that’s required is generally stated on the calibration report or manufacturer’s specifications.
We learn from Ohms Law that when a current flows through a resistor, power is dissipated (I2R). This power causes the sensor to heat; which is known as “self-heating.” When the temperature sensor is calibrated, its self-heating has been accounted for.
When using either sensor type, be sure to set the readout for the proper excitation current. Too little or too much current will cause measurement errors. These sensors can even be damaged if too much current is applied.
Some readouts will automatically choose the proper current when either “thermistor” or “PRT” is selected. Others may need to be set manually. The settings are generally in the probe setup menu. If you select the current manually, always refer to the thermometer’s specifications or calibration report for the proper current.
2. Low insulation resistance and leakage currents
Low insulation resistance is sometimes referred to as shunt resistance, because current is allowed to flow outside of the measurement circuit. Electrically, it is like putting another resistance in parallel with the sensor. When low insulation resistance occurs, too often the transition junction temperature has become too hot. (The hub should not be so hot that it is painful to touch.)
Additionally, low insulation resistance may result if the sheath has been bent, or if the seal has been compromised, allowing moisture to reach the sensor and lead wires. This problem usually can be avoided through proper use and handling.
3. Transition junctions
Thermistors and PRTs generally have transition junctions. The transition junction is where the cable lead wires connect to the sensor lead wires. The lead wires will either be soldered or spot welded. If they are soldered and the junction gets too hot, the solder will melt, causing an open or intermittent condition.
Usually, the junction is sealed with epoxy to keep out moisture and other contaminants. If the seal is subjected to temperatures that are beyond what the epoxy can handle, the seal may crack. This allows moisture and other contaminants to penetrate the seal and reach the lead wires and sensor. Moisture accumulation is most noticeable when the temperature sensor is left to soak at temperatures below ambient or if the ambient humidity is high.
PRTs are often packed with powdered insulative material. This material makes the PRT less susceptible to stress caused by mechanical shock. Unless a good seal exists, at low temperatures the insulation absorbs moisture from the air. Moisture or other contaminants create errors in the measurements and cause the temperature sensor to fail calibration. Trapped moisture can also present a safety concern. If the insulation has absorbed a lot of moisture and the temperature sensor is put into a high-temperature heat source, the moisture will turn to steam, possibly causing the seal to blow or rupture the sheath.
4. Broken or intermittent lead wires
If the temperature sensor cable is pulled, overworked or stressed,
the lead wires may break, causing an open or an intermittent
connection. On occasion, open or intermittent sensor or sensor lead
wires may occur. Some intermittent events are not noticeable until
the temperature sensor is heated, causing the wire to expand and
separate.
Even if great care has been taken to prevent broken or intermittent connections, they still may occur given enough time and use. The repeated expansion and contraction of the lead and sensor wires may eventually take its toll, causing the wire to break.
5. Contamination
Contamination can be caused by chemicals, metal ions or
oxidation.
Chemical contamination can occur in PRTs if a liquid reaches the lead or sensor wires. This can change the purity of the platinum, which alters its electrical characteristics. Any changes in purity will be permanent.
Metal Ion contamination of platinum wire usually occurs at 600 ºC and higher. Because PRT sensors are manufactured using high purity platinum wire, they are the most susceptible to this type of contamination. Metal ion contamination is not reversible and will cause a PRT to constantly drift upwards in temperature. This is particularly noticeable in a triple-point-of-water cell, where the reference temperature is extremely stable. When a PRT is manufactured for extremely high temperatures, it’s constructed in such a way that the sensor is protected from ion contamination.
Temperature sensor sheaths are usually sealed to guard against contamination. Both industrial and secondary temperature sensors are not evacuated before being sealed. Generally, therefore, there will be some dry air inside them. When they are exposed to various temperatures, oxidation can form on the surface of the wire. Oxidation primarily affects temperature sensors whose sensing elements contain platinum wire. Oxidation causes an increase in RTPW (resistance at the water triple point) in metallic RTDs. Fortunately, oxidation can be removed by annealing the RTD, using the manufacturer’s recommended temperature and procedure. Before and after annealing, compare the temperature sensor with a standard of superior accuracy such as a triple point of water cell. This allows you to determine whether the procedure was successful, and it helps you keep a history of the temperature sensor’s performance.
6. Hysteresis and non-repeatability
Hysteresis is a condition in which temperature sensor’s readings lag behind or appear to have a “ memory” effect as the thermometer is moved through a sequential range of temperatures. Measured values depend on the previous temperature in which the sensor or wire was exposed. If a temperature sensor is taken through a range of temperatures for the first time—let’s say, from cold to hot—it will follow a particular curve. If the measurements are repeated in the reverse order, (hot to cold in our example), a thermometer that has a hysteresis problem will have an offset from the previous set of measurements. If repeated, the amount of offset may not always be the same.
Hysteresis does not occur with undamaged standard platinum resistance thermometers (SPRTs), because SPRTs are designed to be strain free. PRTs that are designed to be rugged, however, do not have a strain-free design and have at least some hysteresis. Moisture ingress, or moisture penetrating inside the temperature sensor, causes hysteresis in RTDs of any type.
7. Inhomogeneity
When a thermocouple is used at high temperatures, its wire may become contaminated. This causes the local Seebeck coefficient of the wire to change from its initial state. In other words, this alters the sensitivity of the wire to changes in temperature. However, the temperature exposure and contamination may not be uniform along the length of the thermocouple. The Seebeck coefficient then becomes a function of position along the thermocouple. This leads to measurement errors that depend on the temperature profile the thermocouple is exposed to all along the length of the thermocouple, and not just the temperature at the measurement junction.
8. Short term stability
Measurement repeatability is a term that can be used in many
different ways. It should be defined by the person using the term.
It often refers to the RTPW repeatability during a segment of
thermal cycling or a calibration process.
When a temperature sensor fails to meet its short term stability specification, it means the deviation between measurements at a particular temperature is outside its specification. This could be caused by a large standard deviation or by readings that continually drift in one direction. Potential causes for short-term stability problems include moisture, contamination, strain, leakage current, mechanical shock, and inhomogeneity. Ways to help prevent temperature sensor failure To avoid contamination, take proper precautions when using temperature sensors in harsh environments. Do not subject the transition junction to higher or lower temperatures than the epoxy seal or transition junction can handle. Refer to the temperature sensor’s specifications or contact the temperature sensor manufacturer for the transition junction temperature specification. If there is a possibility that the transition junction could be exposed to high or even marginally high temperatures, a heat shield or heat sink is recommended.
To reduce these limitations
Do not drop, bump, or vibrate a PRT.
Never bend a sheath that isn’t designed to be bent. Even slight
bends may adversely affect the calibration or temperature sensor
life.
Never submerge the transition junction into a liquid.
Never exceed the temperature specification of the temperature
sensor.
Do not soak temperature sensors for long periods of time,
particularly at temperatures where oxidation is likely to
occur.
Do not pull or overly strain the temperature sensor cable.
If a temperature sensor requires annealing, use recommended
temperatures and techniques. Afterward, always verify the
temperature sensors accuracy by comparing it against a primary
standard.
Periodically compare the temperature sensor’s accuracy to a primary
standard, such as a water-triple-point cell or a calibrated SPRT
(standard platinum resistance thermometer).