Question

In: Civil Engineering

Using the absolute volume method, a colleague started a mix design for a simple concrete foundation...

Using the absolute volume method, a colleague started a mix design for a simple concrete foundation in a mild climate and got through Step 5 and has asked you to finish the work. They have already determined the mix needs:
• a w/c ratio of 0.45
• a 2” slump
• 1830 lb of gravel in the oven dry conditions,
• and 3.5% air provided by air entrainer.
The available gravel (coarse aggregate) is subangular with a NMSA = 3⁄4”. It has a specific gravity, Gs = 2.7, with a moisture content of 1.8% and an Absorption of 2.2%. The available sand (fine aggregate) has a specific gravity, Gs =2.45, with a moisture content of 3.8% and an absorption of 2.4%. Gs of cement = 3.15.

For each cubic yard of concrete for this mix, determine:
• the total weight of water, cement, moist sand, and moist gravel required. Don’t worry about the amount of
air entrainer product in fluid ounces.
• Summarize the total mix design (neglecting the required fluid ounces of air entrainer)

Course aggregate:

Fine aggregate:

Cement:

Water:

Solutions

Expert Solution

Ans) Let the total volume of trial mix be 1 cubic yard (27 )  then according to ACI 211.1-91 , table 6.3.3 , for 3/4 in aggregate and 2 in slump , amount of water required per cubic yard of concrete is 280 lb/cy

=> Water requied = 280 lb/cy

Also, Amount of cement = Amount of water / w-c ratio

=> Amount of cement required = 280 lb / 0.45 = 622.22 lb

=> Volume of cement required = Amount / (Specific gravity x 62.4)

=> Volume of cement required = 622.22 / (3.15 x 62.4) = 3.165

Given, amount of coarse aggregate required = 1830 lb

=> Volume of coarse aggregate = Amount / (Specific gravity x 62.4)

=> Volume of coarse aggregate = 1800 / (2.7 x 62.4) = 10.68

Now, according to absolute volume method,

Volume of fine aggregate = Total volume of concrete - Volume of water,cement ,coarse aggregate and air

=> Fine aggregate volume = 27 - [(280/62.4) + 3.165 + 10.68 + 0.035(27)]

=> Fine aggregate volume = 27 - 19.28 = 7.72 ft3

=> Amount of fine aggregate = Volume x Specific gravity x Water unit weight = 7.72 x 2.45 x 62.4 = 1180.23 lb

Correction in mixing water :

Now, since both aggregates has moisture and absorption capacity, so they will absorb some water as well as provide some water to concrete so in order to maintain constant water cement ratio, amount of mixing water needs to be corrected

Water absorbed by coarse aggregate = (0.022 - 0.018) x 1830 lb = 7.32 lb

Water absorbed by fine aggregate = (0.024 - 0.038) x 1180.23 = -16.52 lb

  => Actual amount of water to be added = 280 lb + 7.32 - 16.52 = 270.80 lb

Hence, summary of mix design is as follows :

Component Amount (lb)
Cement 622.22
Water 270.80
Coarse aggregate 1830.00
Fine aggregate 1180.23

Related Solutions

Using the absolute volume method, a colleague started a mix design for a simple concrete foundation...
Using the absolute volume method, a colleague started a mix design for a simple concrete foundation in a mild climate and got through Step 5 and has asked you to finish the work. They have already determined the mix needs: • a w/c ratio of 0.45 • a 2” slump • 1830 lb of gravel in the oven dry conditions, • and 3.5% air provided by air entrainer. The available gravel (coarse aggregate) is subangular with a NMSA = 3⁄4”....
8) Design a concrete mix for the following conditions and constraints using the absolute volume method:...
8) Design a concrete mix for the following conditions and constraints using the absolute volume method: Design Environment : Non-air entrained concrete will be used to cast Concrete frame. Required design strength(5000 psi) Minimum dimension (10 in.) Minimum space between rebars (1.5 in.) Minimum cover over rebars (2.5 in.) Standard deviation of compressive strength (600 psi) , (25 samples) Available Materials Cement Type II , moderate exposure Coarse aggregate Nominal Maximum size 1 in. river gravel (round) Bulk oven dry...
Design a concrete mix for the superstructure of a building using DoE mix design method requiring...
Design a concrete mix for the superstructure of a building using DoE mix design method requiring a characteristic strength of 40MPa at 28days and a slump of 30-60mm. The materials available are ordinary Portland cement, and uncrushed fine and coarse aggregates of specific gravity of 2.65. The maximum nominal size of coarse aggregate is 10mm and fine aggregate confirms to the grading zone III. Neglect the effect of standard deviation and other factors.
Design a concrete mix by using ACI Method of Mix Design having 28-day characteristic mean strength...
Design a concrete mix by using ACI Method of Mix Design having 28-day characteristic mean strength of 28 MPa for a deck of a residential building at Nebraska. Dry weather and gradually warming temperatures may be expected throughout the working week. Fresh concrete composed of a slump of 90 mm and maximum aggregate size of 25 mm. Determine the amount of water reducing admixture to be used for 0.24 % and 0.35 %. Deck is a flat surface capable of...
Q1) Design a concrete mix by using ACI Method of Mix Design having 28-day characteristic mean...
Q1) Design a concrete mix by using ACI Method of Mix Design having 28-day characteristic mean strength of 27 MPa for a deck of a residential building at Nebraska. Dry weather and gradually warming temperatures may be expected throughout the working week. Fresh concrete composed of a slump of 90 mm and maximum aggregate size of 25 mm. Determine the amount of water reducing admixture to be used for 0.24 % and 0.65 %. Deck is a flat surface capable...
Design a concrete mix using ACI Method required for an exterior column to be located above...
Design a concrete mix using ACI Method required for an exterior column to be located above ground level in an area where it will be wet and subjected to substantial freezing and thawing. The concrete is required to have an average 28-day compressive strength of 30 MPa. For the conditions of placement, the slump should be between 25 and 100 mm. The column is 300 mm square with a minimum clear space for aggregate of 50 mm. The properties of...
concrete C25 mix design lab report
concrete C25 mix design lab report
Design a concrete mix for reinforced concrete beams of a structure. The structure is located in...
Design a concrete mix for reinforced concrete beams of a structure. The structure is located in a locality wherein water has excess of chlorides in it. Required average compressive strength of concrete has been determined to be 4700 psi. Beams have cross-section of 9 in. x 21 in. reinforced with 4 # 6 bars. Reinforcement has a concrete cover of 1.25 in. and there is a clear space of 1.0 in. between form surface and steel bars. Fine aggregate has...
I mention everything in detail (Concrete mix design) INTRODUCTION TO REINFORCED CONCRETE
I mention everything in detail (Concrete mix design) INTRODUCTION TO REINFORCED CONCRETE
a. Design a concrete mix for construction of a water tank using ACI Committee 211.1-year 1991....
a. Design a concrete mix for construction of a water tank using ACI Committee 211.1-year 1991. The specified design strength of concrete is 30 MPa at 28 days. Standard deviation can be taken as 4 MPa. The specific gravity of fine aggregate and coarse aggregate are 2.65 and 2.7 respectively. The dry rodded bulk density of the coarse aggregate is 1600 kg/m3 and the fineness modulus of fine aggregate is 2.80. Ordinary Portland cement (Type I) will be used. A...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT