1. In a certain pint in an electrical system, the available fault current is 12 pu. Determine the actual fault current using a base power of 100 MVA and a base voltage of 34.5 kV
2. The positive, negative and zero sequence reactances of a 20 MVA, 13.2 kV synchronous generator are 0.3 pu, 0.2 pu and 0.1 pu respectively. The generator is solidly grounded and is not loaded. A line to ground fault occurs on phase a. Neglect all resistances, determine the fault current.