In: Civil Engineering
A large 20-story steel structure is planned for an office building the Denver Metropolitan. The exploration program revealed that foundation soil comprises of 25-foot clay with undrained shear strength of 1,000 psf overlying a thick stiff clay shale with the undrained shear strength of 3,000 psf. To avoid construction noise, the architect selected 3-ft diameter drilled shaft foundation. The drilled shafts are socketed 15 feet in the stiff clay shale. Calculate:
a. The ultimate capacity of the drilled shaft.
b. Estimate the total structural dead load.
c. Estimate the office building life load.
d. At a factor of safety of 2,5, how many drilled shafts would be required?
Note: When you suspect some missing information, please make reasonable assumption(s) and process with your solution. Clearly show why assumption(s) is needed.
Ans) Given,
Thickness of clay layer = 25 ft
Undrained shear strength of overlying soil = 1000 psf
Undrained shear strength of below soil = 3000 psf
Diameter of drilled shaft(d) = 3 ft
Length of pile(L) = 15 ft
(a) We know,
Ultimate capacity of pile(Q) = Bearing capacity + Skin friction resistance
Q = qb Ab + qs As
Q = C NcAb + C' As
According to Meyerhoff, Nc = 9
C = unit cohesion at base of shaft
C = undrained shear strength/2
C = 1000/2 or 500psf
Ab = (/4) d2
= adhesive factor ( 0.5 for medium stiff clay)
C' =Average Cohesion along pile
C' = 3000/2 or 1500 psf
As = dL
Putting values,
Q = 9C (/4)d2 + 0.5 C' (dL)
Q = 9(500) (0.785 x 9) + (0.5 x 1500 x 3.14 x 3 x 15)
Q = 31792.5 + 105975
Q = 137767.5 psf
Ans b) Assume 1 story dimension as 20ft x 20 ft x 10ft
Unit weight of steel = 500 pcf
Dead load on single story :
Wall load = 4 x 20 x 10 x 500
= 400000 lb/ft
Roof load = 20 x 20 x 500
= 200000 lb/ft
Floor load = 20 x 20 x 500
= 200000 lb/ft
Total dead load = 800000 lb/ft or 800 kips/ft
Weight of machine, appliance etc contribute 50% of total dead load, therefore factored dead load = 1.5 x 800
DL = 1200 kips/ft
For 20 story , DL = 1200 x 20
DL = 24000 kips/ft
Ans c) Live load Calculation for single story
For office building, live load = 500 psf
Live load per unit length = 500/20 lb/ft
Live load = 25 lb/ft
Factored live load = 1.5 x 25 lb/ft
= 37.5 lb/ft
For 20 story , LL = 37.5 x 20
LL = 750 lb/ft
Ans d) Total load required to be resist = DL+LL
= 24000+0.75
= 24000.75 kips/ft
or 24000750 / 20 psf
or 1200037.5 psf
Q =137767.5 psf
FOS = 2.5
Allowable pressure = Q/FOS
= 55107 psf
Load resisted by one shaft = 55107 psf
Load to be resisted = 1200037.5 psf
Number of drilled shaft required = 1200037.5/55107
= 21.7 or 22