Question

In: Civil Engineering

Q1. The short tied column is to be used to support the following factored load and...

Q1. The short tied column is to be used to support the following factored load and moment: P= 1250 kN and M= 250 kN.m [10 marks]. fc=28 MPa fy=420 MPa

a) Determine required dimensions and reinforcing bars using appropriate ACI column approach [2 marks].

b) Determine maximum ACI design axial load strength for selected column [2 marks].

c) Determine balanced failure point on axial moment interaction diagram [2 marks].

d) Determine the tie size and spacing [2 marks].

e) Draw the typical tie arrangements dimensions [2 marks].

Solutions

Expert Solution

a)

e)

b)

c)

design of column based on ACI code is done above.

Steel Ratio Assumption

According to ACI Code 10.9.1, 0.01 < ρg < 0.08

Determination of Concrete Gross Area

According to ACI Code 10.3.6.1,

design strength for tied column, ∅Pn,max = 0.80∅ [0.85f′c(Ag–Ast)+fyAst]

Where, ∅ = 0.65 (ACI Code-02)

consider Pu = ∅ Pn

Pu = 0.80 Ag ∅ [0.85 f′c (1-ρg) + ρg fy]

Selection of Column Size

With the Ag as obtained in step 3 select a square (h2 ) or rectangular (b x h) section, such that the side dimensions are integer multiplier

Check for Steel Ratio

Putting the selected Ag , ρg is calculated. If ρg = 0.01 ≈ 0.08; Design is ok

Otherwise change the column dimension and repeat this step.

Calculation of Reinforcement

Total reinforcement, Ast = Ag * ρg

Now choose required bar size satisfying the ACI Code 10.9.2 requirements i.e. minimum number of bars > 4 Nos.

Selection of Ties

Reinforcement for ties should be selected in accordance with ACI Code 7.10.5.1:

• Use ties of # 3 bar for longitudinal bar up to # 10

• Use ties of # 4 bar for longitudinal bar of # 11, 14, 18 and bundled bar

Determination of Vertical Spacing of Tie

According to ACI Code 7.10.5.2 the vertical spacing shall be smallest of:

• 16 db of longitudinal reinforcement

• 48 db of tie bar

• Least dimension of column section

Arrangement of Ties

ACI Code 7.10.5.3 specifies the arrangement of ties: The ties shall be so arranged that every corner and alternate longitudinal bar shall have lateral support provided by the corner of a tie having an included angle of not more than 135°.No bar shall be farther than 6 in. clear on either side from such a laterally supported bar. Where the bars are located around the periphery of a circle, complete circular ties may be used.


Related Solutions

Design a square tied column to support an axial dead load of (W1) k and an...
Design a square tied column to support an axial dead load of (W1) k and an axial live load of (W2) k. Begin using approximately (X) percent longitudinal steel, a concrete strength of 4,000 psi and Grade 60 steel. Draw the details of reinforcement and check all ACI recommendation. W1 = 220 k W2 = 165 k X = 2%
1) Design a Tied column to support axial Dead load D = 280 K and axial...
1) Design a Tied column to support axial Dead load D = 280 K and axial live load = 500 k, initially assume 2% longitudinal reinforcement f’c = 4000 psi, fy = 60,000 psi. 2) Sketch the column cross-section and show long bars and ties
Design a nonslender column to support the following service loads and moments. The factored ultimate axial...
Design a nonslender column to support the following service loads and moments. The factored ultimate axial force P1= 100 kips, PD= 100 kips, ML= 2500 in.-kips, and MD= 1000in.- kips,. The eccentricity e to geometric centroid = 6 in. Given: f'c = 4000 psi fy = 60,000 psi. Please show all work and explain your steps, please.
Design a circular column, using approximate methods, for a factored load of 80 Kips and a...
Design a circular column, using approximate methods, for a factored load of 80 Kips and a factored moment of 40 Kip-ft. about x and y axes each. The diameter of column is 18". Material strengths are fc' = 4Ksi and fy = 60Ksi. Use appropriate column interaction diagram.
Determine the maximum live load that a column W14x193 could support if the dead load is...
Determine the maximum live load that a column W14x193 could support if the dead load is ten times the live load. Use A-36 with K=1 and L=22 ft.
A 450 mm × 650 mm column supports factored axial load of 2500 kN centered in...
A 450 mm × 650 mm column supports factored axial load of 2500 kN centered in single footing. After assuming the depth and density of soil above footing, assume the required depth of footing [10 marks]. a) Check depth due to two-way shear b) Check depth due to one-way shear action c) Calculate the bending moment and steel reinforcement e) Determine development length of dowels d) Check bearing stress e) Determine development length of dowels
Prompt: Design the representative column for the factored axial load only. Assume pin connections top and...
Prompt: Design the representative column for the factored axial load only. Assume pin connections top and bottom. If you want, you might consider designing for 75% of capacity, to allow for remaining capacity for the lateral loads to be determined in the future. I'm Suppose to design a Concrete Column; many assumptions can be made, such as type/strength of concrete. The calculated axial load: Pu= 88.2 Kips
Design a RC wall of 4.6m height to support a factored load of 650 KN/m and...
Design a RC wall of 4.6m height to support a factored load of 650 KN/m and factored moment of 30 KNm at right angles to the length of wall. The distance between cross wall is 4m. Sketch the reinforcement details.
A square tied column with f’c=5 ksi and steel with fy=60 ksi sustains an axial load...
A square tied column with f’c=5 ksi and steel with fy=60 ksi sustains an axial load of 225 kips dead load and 375 kips live load and a bending moment of 110 kip-ft dead load and 160 kip-ft live load. Determine the minimum size column and its reinforcement.
steel structure Q1. The column carries 60 kips dead load and 40 kips live load, its...
steel structure Q1. The column carries 60 kips dead load and 40 kips live load, its length is 20 ft, and the steel is A992. Assume the member as pinned at the top and bottom. (a) Compute Pa; (b) Determine the effective length (KL); (c) Use ASD method to select the lightest W section; (d) Check the local buckling slenderness limits of the selected section.