Question

In: Mechanical Engineering

A refrigeration system with a flash chamber operates with R134a between the pressure limits of 1.0...

A refrigeration system with a flash chamber operates with R134a between the pressure limits of 1.0 and 0.1 MPa. The refrigerant leaves the condenser as saturated liquid and is throttled to a flash chamber operating at 0.4 MPa. The refrigerant leaving the low-pressure compressor at 0.4 MPa is also routed to the flash chamber. The vapor in the flash chamber is then compressed to the condenser pressure by the high-pressure compressor, and the liquid is throttled to the evaporator pressure. Assume the refrigerant leaves the evaporator as saturated vapor and compressors are isentropic. (The pressures are absolute pressures)

  1. Draw P-h diagram for the refrigeration cycle on the attached P-h diagram.
  2. The fraction of the refrigerant vapor enters the flash chamber after the first throttle valve.
  3. The enthalpy of the refrigerant vapor at the flash chamber (where the two streams of vapor meet).
  4. The amount of heat removed from the refrigerated space for a mass of 0.5 kg/s through condenser.
  5. The power input to the compressors.
  6. The coefficient of performance for the refrigeration system.

Solutions

Expert Solution

A Refrigeration system with a flash chamber diagram has shown below -

Specific heat capacity ratio for R134a refrigerant -

Now for High-pressure compressor-

Point 4 in the above diagram is slightly superheated.

Refrigerant R134a has a low discharge temperature. Therefore we can say that Intercooling of refrigerant vapor is not possible with a water-cooled heat exchanger, which is generally used for Ammonia refrigerant (because of its high discharge temperature).

b)

Suppose mass flow rate through 1st stage = 1 Kg/sec

From energy balance -

   (1)

(2)

By Solving equation 1 and 2,

Therefore

We know that,

Therefore,

c)

Mentioned in the diagram-

i.e. 410 KJ/Kg

d)

We have,

          (1)

    (2)

     

      (1)

   (2)

(2) - (1) - We get,

Amount of heat removed from refrigerated space =

e)

Power input to the compressor -

If

Then

Therefore,

f)

Coefficient of Performance - COP =

If you have any doubt please ask.


Related Solutions

An ideal vapor compression refrigeration cycle with R134a as the working fluid operates between the pressure...
An ideal vapor compression refrigeration cycle with R134a as the working fluid operates between the pressure limits of 200 kPa and 1200 kPa. Determine a) the mass fraction of the refrigerant that is in the liquid phase at the inlet of the evaporator, and b) the amount of heat transfer (in kJ/kg) to the refrigerant in the evaporator (??).
Consider a two-stage cascade refrigeration system operating between the pressure limits of 1.2 MPa and 200...
Consider a two-stage cascade refrigeration system operating between the pressure limits of 1.2 MPa and 200 kPa with refrigerant R717 (Ammonia) a as the working fluid. The refrigerant leaves the condenser as a saturated liquid and is throttled to a flash chamber operating at 0.45 MPa. Part of the refrigerant evaporates during this flashing process, and this vapor is mixed with the refrigerant leaving the low-pressure compressor. The mixture is then compressed to the condenser pressure by the high-pressure compressor....
4. A two-stage cascade cooling system operates between the pressure limits of 1 and 0.1 MPa....
4. A two-stage cascade cooling system operates between the pressure limits of 1 and 0.1 MPa. Each stage operates on the ideal vapor compression cooling system and the refrigerant R-134a is used as working fluid. The heat transfer from the lower to the upper cycle takes place in an adiabatic reverse flow heat exchanger where both streams enter about 0.4 MPa. The refrigerant mass flow rate is 0.24 kg / s throughout the upper cycle. a. sub-loop mass flow rate...
A steam Rankine cycle operates between the pressure limits of 1500 psia in the boiler and...
A steam Rankine cycle operates between the pressure limits of 1500 psia in the boiler and 1 psia in the condenser. The turbine inlet temperature is 800°F. The turbine isentropic efficiency is 90 percent, the pump losses are negligible, and the cycle is sized to produce 2500 kW of power. Calculate the mass flow rate through the boiler, the power produced by the turbine, the rate of heat supply in the boiler, and the thermal efficiency. Use steam tables
An ideal Rankine cycle operates between the pressure limits of 15 MPa in the boiler and...
An ideal Rankine cycle operates between the pressure limits of 15 MPa in the boiler and 50 kPa in the condenser. The boiler generates steam at a mass flow rate of 50 kg/s and it enters the turbine at a temperature of 1100 °C. a) Calculate the net output of the cycle b) Calculate the thermal efficiency of the cycle.
A simple ideal Rankine cycle with water as the working fluid operates between the pressure limits...
A simple ideal Rankine cycle with water as the working fluid operates between the pressure limits of 4 MPa in the boiler and 5 kPa in the condenser and a turbine inlet temperature of 700°C. The boiler is sized to provide a steam flow of 50 kg/s. Determine the power produced by the turbine and consumed by the pump. Use steam tables. Find the values of power produced by the turbine and consumed by the pump in kW
A gas-turbine power plant operates on the simple Brayton cycle between the pressure limits of 100 and 1200 kPa.
A gas-turbine power plant operates on the simple Brayton cycle between the pressure limits of 100 and 1200 kPa. The working fluid is air, which enters the compressor at 300K at a rate of 150 m3/min and leaves the turbine at 773K. Using variable specific heats for air and assuming a compressor isentropic efficiency of 82 percent and a turbine isentropic efficiency of 88 percent, determine: (a) the net power output (b) the back work ratio (c) the thermal efficiency
An air conditioner using R134a as the working fluid operates on an ideal vapour compression system...
An air conditioner using R134a as the working fluid operates on an ideal vapour compression system between 0.3 and 0.8 MPa. If the specified capacity for air conditioning is 20 kW. What would be its capacity for food freezing for which the evaporator temperature -20oC. Show the cycle on a PH diagram and explain the effect of the changes to the compressor and condenser respectively.
An air-conditioning system operates at a total pressure of 1 atm and consists of a heating...
An air-conditioning system operates at a total pressure of 1 atm and consists of a heating section and an evaporative cooler. Air enters the heating section at 15°C and 55 percent relative humidity at a rate of 30 m3/min, and it leaves the evaporative cooler at 25°C and 45 percent relatively humidity. Using appropriate software, study the effect of total pressure in the range 94 to 100 kPa and plot the results as functions of total pressure. (Please upload your...
An air-standard Carnot cycle is executed in a closed system between the temperature limits of 350...
An air-standard Carnot cycle is executed in a closed system between the temperature limits of 350 and 1200 K. The pressures before and after the isothermal compression are 150 and 300 kPa, respectively. If the net work output per cycle is 0.5 kJ, determine (a) the maximum pressure in the cycle, (b) the heat transfer to air, and (c) the mass of air. Assume variable specific heats for air.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT