The vapor compression (VC) cycle system consists of seven
stages. Two of which are sub-cooling and superheating.
- Additional temperature decrease during conversion of vapor to
liquid which involves removal of heat from the refrigerant at its
saturation condensing temperature is called
sub-cooling. It happens in the system’s
condenser.
- Additional temperature increase above the boiling point during
conversion of the refrigerant from liquid to vapor which involves
addition of heat to the liquid at its saturation temperature is
called superheating. It happens in the system’s
evaporator.
Answer (1):
VC cycle systems typically use 10 to 20 degrees Fahrenheit of
sub-cooling
- Refrigerant normal cooling temperature is between 10 to 20
degrees.
- When the temperature falls below 10 degrees:
- Refrigerant didn’t lose ‘normal heat amount’ during its flow
through condenser.
- When the temperature rises above 20 degrees:
- Refrigerant got cooled more than that of normal.
- A few consequences of improper cooling temperature are as
follows:
- Overcharge
- Undercharge
- Insufficient condenser airflow
Answer (2):
VC cycle systems typically use 10 to 20 degrees Fahrenheit of
super heating
- The normal 10 to 20 degrees temperature make sure that the
compressor draws only vapor (no liquid refrigerant).
- When the temperature falls below 10 degrees:
- It implies that refrigerant didn’t have enough heat in the
evaporator to fully boil into vapor.
- Liquid refrigerant will be drawn which causes:
- Slugging (damage of the compressor valves)
- Premature failure (if mixed with oil)
- When the temperature rises above 20 degrees:
- It implies that refrigerant got more heat than normal, which
may lead to:
- System undercharge
- Refrigerant restriction
- Excessive evaporator heat loads