Question

In: Electrical Engineering

A 45-MVA, 13.8 kV synchronous machine is operating as a synchronous condenser, as discussed in Appendix...

A 45-MVA, 13.8 kV synchronous machine is operating as a synchronous
condenser, as discussed in Appendix D (section D.4.1). It’s short-circuit ratio
is 1.68 and the field current at rated voltage, no load is 490 A. Assume the
generator to be connected directly to an 13.8 kV source

a. What is the saturated synchronous reactance of the generator in per unit
and in ohms per phase?
The generator field current is adjusted to 260 A.
b. Draw a phasor diagram, indicating the terminal voltage, internal voltage,
and armature current.
c. Calculate the armature current magnitude (per unit and amperes) and its
relative phase angle with respect to the terminal voltage.
d. Under these conditions, does the synchronous condenser appear inductive
or capacitive to the 11.5 kV system?

Solutions

Expert Solution

Short circuit ratio is given as

Single phase rated voltage is given by

Single phase rated power is given by

Now, base value of impedance is

Now, base value of current is given by

a.

The saturated synchronous reactance in per units is given by

The saturated synchronous reactance in ohms per phase is given by

b.

where, is armature current

is internal voltage

is external votage

is synchronous saturated reactance

c.

Since generator field current is adjusted to 260 A, internal voltage in per unit will, therefore, be

Rated terminal voltage in per unit is

Now, armature current in per unit value is given by

and armature current in amperes is given by

d.

In this part 11.5 kV sytem is given whereas in rest of the question 13.8 kV system is provided. So, I think there must be some mistake.


Related Solutions

2) A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and...
2) A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has reactance of 1.65 pu. The generator is operated on an infinite bus of 15 kV voltage and delivers 100 MVA at 0.8 Power Factor, lagging. a)Determine the internal voltage (E_i), the power angle (δ), and the line current of the machine. b)If the field current of the machine is reduced by 10%, while the mechanical power input to the machine is maintained constant,...
A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has...
A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has reactance of 1.65 pu. The generator is operated on an infinite bus of 15 kV voltage and delivers 100 MVA at 0.8 Power Factor, lagging. a)Determine the internal voltage (E_i), the power angle (δ), and the line current of the machine. b)If the field current of the machine is reduced by 10%, while the mechanical power input to the machine is maintained constant, determine...
6.9 A3 ϕ, 11 kV, 60 Hz, 25 MVA, Y-connected cylindrical-rotor synchronous machine generator has Ra...
6.9 A3 ϕ, 11 kV, 60 Hz, 25 MVA, Y-connected cylindrical-rotor synchronous machine generator has Ra = 0.45 Ω per phase and Xs = 4.5 Ω per phase. The generator delivers the rated load at 11 kV and 0.85 lagging power factor. Determine the excitation voltage, Ef, for this operating condition. 6.11 The synchronous machine in Problem 6.9 is operated as a synchronous motor and it is drawing rated MVA at 0.85 lagging power factor. Determine the excitation voltage, Ef,...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT