Here are some specific applications where HVDC transmission
provides some technical and economical benefits compared to AC
transmission schemes :
- The potential for long distance transmission,
in particular for long undersea/underground cables transmission
schemes (typically when there is a long submarine cable link >40
km). Long undersea/underground high-voltage cables have a high
electrical capacitance compared with overhead transmission lines
because the conductors within the cable are surrounded by a thin
layer of insulation. The geometry is that of a long co-axial
capacitor. Thus, the total capacitance increases with the
lenght of the cable. This implies that the maximum
feasible length and power transmission capacity of HVAC cable is
limited. As AC cable lenght and voltage increases,
the capacitance and hence the AC charging current
increases in proportion (the charging current is the
current flowing just to charge the line capacitance and is equal to
the line to ground voltage divided by the cable’s capacitive
reactance that is 1/jCw). Where alternating current is used for
cable transmission,charging current is so significant that it
reduces the capability of the line to carry useful current to the
load at the remote end. There is only reactive power and no real
active power can be transmitted. Thus, the reactive
power that is inherently generated in HV cables under AC
voltage increases with both the voltage level and the cable length.
For increasing transmission distances and voltage
levels, reactive power compensation will
be required at both cable ends to product active
power. The absence of compensators on DC
linesmakes it possible to realize several hundred of
kilometers of undersea links without technical constraint.
- Lower energy losses : HVDC comprises
active power only and causes 20% lower
losses than HVAC which comprises reactive power. In the
case of HVAC cables, the additional current flowing in the cable to
charge its capacitance causes added energy loss via dissipation of
heat in the conductors of the cable, raising its temperature
(dielectric losses or heating
effectin the cable insulation). Under AC these losses are
mainly related to the skin effect that is absent
under DC voltage. Let’s remind that the skin effect is the tendency
of an alternating current to become distributed within a conductor
such that the current density is largest near the surface of the
conductor, and decreases with greater depths in the conductor. The
electric current flows mainly at the "skin" of the conductor,
between the outer surface and the skin depth. The skin effect
causes the effective resistance of the conductor to increase at
higher frequencies where the skin depth is smaller, thus reducing
the effective cross-section of the conductor (R=pl/S). Therefore,
for the same conductor losses, a given conductor can carry
more currentto the load when operating with HVDC than with
HVAC.
- Asynchronous connection : HVDC allows
power transmission between unsynchronized AC distribution
systems and is able to transfer power between countries
that use AC at different frequencies! For example it allows the
connection of 50Hz and 60Hz networks. Because the transfer can
occur in both directon, it increases the stability of both
networks by allowing them to draw on each other in
emergencies and failures.
- Integration of renewable resources such as
wind into the transmission grid is an other area for HVDC
applications that is growing around the world.
Many countries are considering building HVDC systems at voltage
level of +800kV and above, creating a need for additionnal
research to develop components to operate at these Ultra
High Voltage (UHV) level. In countries such as India, China, Brazil
and South Africa, the demand for power is growing
and there is a need to transmit power with UHV DC lines over
1000–2000 km at 800kV. However it may take a while for North
America and Europe to consider UHV DC tranmission as they have less
need for large amounts of power transfer over long distances.
Conclusion : The use of HVDC for future transmission is
growing faster than ever for economic and
technical reasons. HVDC transmission has low
environmental impact and is the only technical
solution for long links. These features are turning HVDC
links to be the preferred choice for grid interconnection. Given
the increasing importance of HVDC networks, diagnostic
techniques able to infer degradation processes and prevent
failures are becoming more and more important. These techniques
focuses especially on Partial Discharges detection
in insulating cables under HVDC conditions because Partial
Discharge phenomenon is considered as one of the main cause of
degradation of insulators in High Voltage cables.