Question

In: Chemistry

Chemical Engineering question. Air at 38.0°C and 99.0% relative humidity is to be cooled to 18.0°C...

Chemical Engineering question.

Air at 38.0°C and 99.0% relative humidity is to be cooled to 18.0°C and fed into a plant area at a rate of 710.0 m3/min. You may assume that the air pressure is 1 atm in all stages of the process.
A.) Calculate the rate at which water condenses in kg/min .

B.) Calculate the cooling requirement in tons (1 ton of cooling = 12,000 Btu/h), assuming that the enthalpy of water vapor is that of saturated steam at the same temperature and the enthalpy of dry air is given by the expression H∧ (kJ/mol) = 0.0291[T(°C) – 25].

Solutions

Expert Solution

A)Vapor pressure data (mm Hg)   : 38 deg.c= 49.7 and 18 deg.c = 15.5 mm Hg

Flow rate of air water vapor mixture= 710m3/min=710*1000L/min= 7.1*105 L/min

Relative humidity = 100*partial pressure of water vapor/vapor pressure of liquid

Hence at 38 deg.c, 0.99= partial pressure of water vapor/49.7

Partial pressure of water vapor= 49.7*0.99=49.2 mm Hg

Total moles of air vapor mixture from gas law, n= PV/RT, where P= 1atm, R=0.0821 L.atm/mole.K, T= 38 deg.c= 38+273=311K

Hence no of moles of air water vapor mixture = 1*7.1*105/(0.0821*311)= 27807 moles/min

At inlet conditions of 38 deg.c

Moles of water vapor/total moles = partial pressure of water vapor/total pressure

Moles of water/ 27807= 49.2/760= 0.065

Moles of water vapor at inlet= 27807*0.065=1807 moles/min

Moles of dry air at inlet= 27807-1807=26000 moles/min. This remains the same through out the cooling process and is considered as tie substance.

At outlet, the air is assumed to be saturated with water vapor. Hence at the exit temperature of 18 deg.c, partial pressure of water vapor= vapor pressure of water =15.5 mm Hg

Hence partial pressure of water vapor/ partial pressure of dry air= moles of water vapor/ moles of dry air

15.5/(760-15.5)= moles of water vapor/26000

Moles of water vapor at the exit/min= 541 moles/min

Moles of water condensed/min= molar flow rate of water vapor at the inlet- molar flow of water vapor at the exit= 1807-541=1266 moles/min

Mass flow rate of water condense= molar flow rate of water condensed*molar mass = 1266*18 g/min=22788g/min= 22.788 kg/min

Enthalpy of mixture at the inlet at 38deg.c= enthalpy of dry air + enthalpy of water vapor

Enthalpy of mixture at the outlet at 18 deg.c= enthalpy of dry air+ enthalpy of water vapor

Enthalpy change= Enthalpy of dry air at inlet- enthalpy of dry air at outlet+ enthalpy of water

Condensed=

latent heat of vaporization of water= 40.7 KJ/moe

enthalpy change = cooling requirement {0.0291*(38-25)- 0.0291*(18-25)}26000Kj+40.7*1266= 66658.2Kj/min=1111 Kj/hr

1Btu= 1.05 KJ

Hence 1111 Btu/hr= 1111*1.05 Kj/hr =1166.55 Btu/hr

1Ton=12000 Btu/hr

Hence Tonnage= 1166.55/12000 =0.097 Tons


Related Solutions

Air at 38.0°C and 99.0% relative humidity is to be cooled to 16.0°C and fed into...
Air at 38.0°C and 99.0% relative humidity is to be cooled to 16.0°C and fed into a plant area at a rate of 510.0 m3/min. You may assume that the air pressure is 1 atm in all stages of the process. Calculate the rate the water condenses in kg/min.
Humid air at 155 kPa, 40°C, and 70 percent relative humidity is cooled at constant pressure...
Humid air at 155 kPa, 40°C, and 70 percent relative humidity is cooled at constant pressure in a pipe to its dew-point temperature. Calculate the heat transfer, in kJ/kg dry air, required for this process. Use data from the tables. The heat transfer is  kJ/kg dry air.
15 m3 /min of air at 104o F and 60% relative humidity is cooled to 59o...
15 m3 /min of air at 104o F and 60% relative humidity is cooled to 59o F and 100% relative humidity, and then reheated to 68o F. Find the following: a. The flow rate of dry air (BDA) in kg /min. b. The amount of water condensed during cooling stage. c. kW of power needed for cooling the air in the cooling stage. d. kW of power needed for the heating step.
If at 30F the air has 25% relative humidity, what is the relative humidity at 70F...
If at 30F the air has 25% relative humidity, what is the relative humidity at 70F and how much moisture must be added to get it up to 50% relative humidity.
Air at 35°C and 33% relative humidity is used for drying a food product. The air...
Air at 35°C and 33% relative humidity is used for drying a food product. The air is first heated to 90°C and then cooled adiabatically to an exit dry bulb temperature of 40°C. (a) How much moisture did the air pick up? (b) Calculate the change in enthalpy from the initial unheated air to the final moist air. (c) If the food is dried from 85% moisture to 20% moisture (both on a wet basis) at an inlet flow rate...
At 200 C relative humidity of 1 m3 of air is 60%. when temperature is kept...
At 200 C relative humidity of 1 m3 of air is 60%. when temperature is kept constant and volume is reduced to 0.25 m3 find the mass of moist air that would be condensed. SVP of water at 200 C = 17.5mmHG R= 8.31 J mol-1 K-1
Humid air at 300 kPa, 10°C, and 90% relative humidity is heated in a pipe at...
Humid air at 300 kPa, 10°C, and 90% relative humidity is heated in a pipe at constant pressure to 50°C. Calculate the amount of heat, in kJ/kg dry air, required
I need answers on 3.2.4 3.2.3 If the air temperature is 15°C and the relative humidity...
I need answers on 3.2.4 3.2.3 If the air temperature is 15°C and the relative humidity 35 percent, calculate the vapor pressure, specific humidity, and air density. Assume standard atmospheric pressure (101.3 kPa). 3.2.4 Solve Prob. 3.2.3 if the air temperature rises to 300C. By what percentage does the specific humidity increase as a result of the temperature rise from 15 to 300C?
Relative humidity isn't everything. Why is it that outdoor air of 80 Fo at 55% humidity...
Relative humidity isn't everything. Why is it that outdoor air of 80 Fo at 55% humidity will feel more “muggy” than a 50 Fo cave at 75% humidity? What other parameter is a better measure of the actual amount of moisture in the air, and how do we define it? Then give two examples of when keeping close track of moisture in the air is important.
Relative humidity isn't everything. Why is it that outdoor air of 80 Fo at 55% humidity...
Relative humidity isn't everything. Why is it that outdoor air of 80 Fo at 55% humidity will feel more “muggy” than a 50 Fo cave at 75% humidity? What other parameter is a better measure of the actual amount of moisture in the air, and how do we define it? Then give two examples of when keeping close track of moisture in the air is important.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT