Question

In: Physics

The air-conditioned room which stands in a ventilated basement measuring length, width, height 6m x 3m...

The air-conditioned room which stands in a ventilated basement measuring length, width, height 6m x 3m x 3m. one of the two 3m walls faces west and has a double glass window measuring 1.5 m x 1.5 m, mounted on a wall without external shading. There is no heat gain through the wall other than the wall facing west. Calculate sensible heat, latent heat, and total heat in the room. How much cooling capacity is needed?

Inside conditions: 25 Celsius drybulb, 50% RH
Outside conditions: 43 Celsius dry bulb, 24 Celsius wetbulb
U-Value for walls: 1.78 W / m ^ 2.K
U-Value for roof: 1,316 W / m ^ 2.K
U-Value for floors: 1.2 W / m ^ 2.K
Effective Temp.Difference (ETD) for walls: 25 Celsius
Effective Temp.Difference (ETD) for roof: 20 Celsius
U-Value for glass: 3.12 W / m ^ 2.K
Solar Heat Gain (SHG) for glass: 300 W / m ^ 2
Internal shading coefficient (SC) for glass: 0.86
Occupants: 4 (90W sensible heat / person) (40W latent heat / person)
Lamp load: 33 W / m ^ 2 of floor area
Equipment load: 600 W (Sensible) + 300W (latent)
Infiltration: 0.5 Air Changes per Hour
Barometric pressure: 101 kPa
CLF: 1

Please Helpme to Answer this Question

Solutions

Expert Solution

Sol:

From the psychrometric chart,

For the inside conditions of dry bulb, 50 percent RH:

For the outside conditions of   dry bulb, wet bulb:

density of dry air = 1.095 kg / m3

External loads:

a) Heat transfer rate through the walls: Since only the west wall measuring 3m x 3m with a glass window of 1.5m x 1.5m is exposed; the heat transfer rate through this wall is given by:

(Sensible)

b) Heat transfer rate through the roof:

  (Sensible)

c) Heat transfer rate through the floor: Since the room stands on a well-ventilated basement, we can assume the conditions in the basement to be same as that of the outside (i.e., dry bulb and wet bulb), since the floor is not exposed to solar radiation, the driving temperature difference for the roof is the temperature difference between the outdoor and indoor, hence:

(Sensible)

d) Heat transfer rate through a glass: This consists of the radiative as well as conductive components. Since no information is available on the value of CLF, it is taken as 1.0. Hence the total heat transfer rate through the glass window is given by:

(Sensible)

e) Heat transfer due to infiltration: The infiltration rate is 0.5 ACH, converting this into mass flow rate, the infiltration rate in kg/s is given by:

minf = density of air x (ACH x volume of the room) / 3600

Sensible heat transfer rate due to infiltration, Qs,inf;

(Sensible)

Latent heat transfer rate due to infiltration, Ql,inf:

(Sensible)

Internal loads:

a) Load due to occupants: The sensible and latent load due to occupants are:

Qs,occ = no.of occupants x SHG = 4 x 90 = 360 W

Ql,occ = no.of occupants x LHG = 4 x 40 = 160 W

b) Load due to lighting: Assuming a CLF value of 1.0, the load due to lighting is:

Qlights = 33 x floor area = 33 x 18 = 594 W (Sensible)

c) Load due to appliance:

Qs,app = 600 W (Sensible)

Ql,app = 300 W (Latent)

Total sensible and latent loads are obtained by summing-up all the sensible and latent load components (both external as well as internal) as:

Qs,total = 300.38+473.76+388.8+706.9+151+360+594+600 = 3574.84 W (Ans.)

Ql,total = 16.4+160+300 = 476.4 W (Ans.)

The total load on the building is:

Qtotal = Qs,total + Ql,total = 3574.84 + 476.4 = 4051.24 W (Ans.)

Room Sensible Heat Factor (RSHF) is given by:

RSHF = Qs,total / Qtotal = 3574.84 W / 4051.24 W = 0.882 (Ans.)

To calculate the required cooling capacity, one has to know the losses in return air ducts. Ventilation may be neglected as the infiltration can take care of the small ventilation requirement. Hence using a safety factor of 1.25, the required cooling capacity is:

Required cooling capacity = 4051.24 x 1.25 = 5064.05 W      (Ans.)


Related Solutions

The length, width, and height of a room are measured to be 4.1 meters, 3.2 meters,...
The length, width, and height of a room are measured to be 4.1 meters, 3.2 meters, and 2.4 meters, respectively. Each measurement is subject to a 1% error. Find the volume of the room and it’s uncertainty in cubic meters. Assume that the percentage errors add. Express the answer with the appropriate number of significant digits.
Water flows at a rate of 6m^3 / s in a rectangular channel of 3m width...
Water flows at a rate of 6m^3 / s in a rectangular channel of 3m width and 60cm water depths . Check whether the hydraulic jump occurs or not . If it is occurred , then determine the total energy loss during the jump and the jump efficiency . What is the type of this jump ? Question by hydraulic structures material Theme Hydraulic Jump
A Tank with a dimension of length (L) x width (B) x height (H) of 4m...
A Tank with a dimension of length (L) x width (B) x height (H) of 4m x 2m x 2m is filled with 1m depth of water and with oil to the fullest. Density of oil ρm= 801 kg/m3. The tank is open. 1.Calculate and draw pressure distribution on tank wall 2.Calculate force on the length and width side of tank wall, also on the bottom of the tank Given: ρwater= 1000 kg/m3 , g = 9,81 m/sec2
An air tight laboratory is 4 m long and 3m wide and 3m high. the room...
An air tight laboratory is 4 m long and 3m wide and 3m high. the room is under normal atmospheric pressure and has a temperature of 20C A 10kg block of dry ice is then left in the room and evaporated into carbon dioxide gas molecular mas 44u. assuming that the temperature of the room does not change appreciably what will it's final pressure be ? stay out of the room as you may die from hypercapnia or carbon dioxide...
An air-conditioned room is to be maintained at 18oC, percentage saturation 40%. The fabric heat gains...
An air-conditioned room is to be maintained at 18oC, percentage saturation 40%. The fabric heat gains are 3000 W and there are a maximum of 20 people in the room at any time. Neglecting all other heat gains or losses calculate the required volume flow rate of air to be supplied to the room and its percentage saturation when the air supply temperature is 10oC. (Sensible heat gains per person = 100 W; latent heat gains per person = 30W;...
A fluidic storage tank has a square cross-section (3m x 3m) and a height of 10m....
A fluidic storage tank has a square cross-section (3m x 3m) and a height of 10m. The tank is half-filled with a fluid with the density of 200kg/m3. The tank suddenly develops a leak. A sensor inside the tank instantaneously alerts the owner that the height of the fluid in the tank is decreasing by 1mm/min. Find the flow rate out of the tank at that moment in time.
The length, width, and height of a box are measured as 5 ft, 4 ft, and...
The length, width, and height of a box are measured as 5 ft, 4 ft, and 8 ft, respectively, with an error in measurement of at most 0.3 ft in each. Use differentials to estimate the maximum error (in feet) in the calculated volume of the box.
The length ℓ, width w, and height h of a box change with time. At a...
The length ℓ, width w, and height h of a box change with time. At a certain instant the dimensions are ℓ = 4 m and w = h = 1 m, and ℓ and w are increasing at a rate of 8 m/s while h is decreasing at a rate of 2 m/s. At that instant find the rates at which the following quantities are changing. (a) The volume. (b) The surface area. (c) The length of a diagonal....
The length l, width w, and height h of a box change with time. At a...
The length l, width w, and height h of a box change with time. At a certain instant the dimensions are l = 2 m and w = h = 3 m, and l and w are increasing at a rate of 7 m/s while h is decreasing at a rate of 5 m/s. At that instant find the rates at which the following quantities are changing. (a) The volume. m3/s (b) The surface area. m2/s (c) The length of...
Design a rectangular milk carton box of width w, length ll, and height h which holds...
Design a rectangular milk carton box of width w, length ll, and height h which holds 540 cm^3 of milk. The sides of the box cost 1 cent/cm^2 and the top and bottom cost 3 cent/cm^2. Find the dimensions of the box that minimize the total cost of materials used.