In: Electrical Engineering
delta to wye transformer. with the following voltages
what is the phase to ground voltage.
A: 345kv
B: 115kv
C: 34kv
D: 12kv
do the same voltages for wye to delta, delta to delta
and wye to wye transformer.
please show your work. so i could understand the math behind
it.
thank you.
345kv primary to 115kv secondary
115kv primary to 34.5kv secondary
34.5kv primary to 12kv secondary
Please note the following three facts ==>
1. All the possible transformer combinations can be calculated with the help of above 8 cases.
2. Vp is phase to neutral voltage in all the cases. In case of star winding, we ground the neutral. So, in case of star winding, phase to ground voltage = Vp.
3. In case of delta winding, the neutral is not accessible. So, we can't ground the neutral. If you measure phase to ground voltage, then that particular phase will also become grounded. So, the ideal phase to ground voltage measurement value should be zero. But, if you can access the neutral of a delta winding and ground it, then phase to ground voltage = Vp.
NOTE - Hope the answer helps. Please let me know in the comments for more help.