In: Mechanical Engineering
Using the Lumen Method to find out how many fittings are
required for a square conference room which requires 500 lux from
CIBSE Guide, of area 200 m2, using the T5 fluorescent fittings at
1.2 meter long each and at 2 m high measured from the light source
to the working surface.
The 1.2m T5 luminaire has 2700 lumens each.
Your answer should mention about all the light losses, say, due to
surface reflectance at ceiling, wall and floor, light loss factor,
maintenance factor, etc,.
Steps to be followed in Lumen Method
1. Assign required lux level
2. Select luminaire
3. Determine room index
4. Determine number of fixtures
N- Number of lamps required
E- Illuminaire level
A- Area at working p;ane
F- Average luminux flux from each lamp
UF – Utilisation factor
MF-Maintenance factor
Given
E= 500 lux
A= 200m2
F= 2700 lumens
To find utilization factor room index to be found out
Room index
Since is is square room
L=W= 14.14 m
H=2m given
From the Surface illuminated table For Reflectance 70% in
ceiling,30% in Wall and 20% in floor
The value of UF =0.64
Assuming the Maintenance factor as 0.8
Number of luminaire
N= 72