Question

In: Chemistry

1000 m3 of moist air at 101 kPa and 25 °C with a dew point of...

1000 m3 of moist air at 101 kPa and 25 °C with a dew point of 11 °C enters a process. The air leaves the process at 98 kPa with a dew point of 58 °C. Assume ideal gases.

(a) Draw and label a flowsheet for the process.

b) What is the mole fraction of water in the air entering the process? Leaving the process?

(c) How many moles of water are added to or removed from the 1000 m3 of moist air?

Solutions

Expert Solution

Dew point is the temperature at which the partial pressure of vapour =vapour pressure of liquid at the given temperature

Vapor pressure of water

11 deg.c =9.8 mm Hg

55 deg.c =118 mmHg

101 Kpa= 0.9967 atm

98 Kpa =0.9672 atm

Partial pressure of water =9.8 mm Hg

Mole fraction of water vapour= Moles of water vapor/ total moles

Partial pressure of water vapour= Mole fraction * Total pressure of water vapor

At inlet

Partial pressure of water vapour= 9.8/760 mm Hg

Mole fraction of water vapour =(9.8/760)/ 0.9967 =0.013

At out let.

Mole fraction of water vapour= (118/760)/0.9672 =0.1605

Since there is an increase in mole fraction of water vapor at the outlet, Moisture is added to air.

Total moles of wet air entering per 1000m3 of wet air can be calculated from

PV= nRT, R=0.08206 L.atm/mole.K

n= PV/RT= 1000*1000L*0.9967 atm/(0.08206*(25+273.15)=40737 moles =40.737 Kg moles

Moles of water/ Moles of wet air =Mole fraction

At inlet

Moles of water = Mole fraction* Moles of wet air= 0.013* 40.737 kg moles=0.53 kg moles

Moles of dry air =Moles of wet air-moles of water vapour= 40.737-0.530= 40.207 Kg moles

These moles remain the same at the outlet as well

Mole fraction of dry air at the out let= 1-Mole fraction of water vapour

= 1-0.1605 =0.8395 moles

Mole fraction= Moles of dry air/ Total moles

Moles of dry air =40.207

Total moles of wet air at the outlet= 40.207/0.8395=48.53Kg moles

Moles of water vapour added = Moles of air at outlet- Moles of air at inlet= 48.53-40.737 =7.793Kg moles


Related Solutions

One hundred moles of moist air (100 moles) at 25oC and 100 kPa has a dew...
One hundred moles of moist air (100 moles) at 25oC and 100 kPa has a dew point of 16oC. If you want to remove 50% of the initial moisture in the air (at a constant pressure of 100 kPa). 1. Sketch the process. 2. Determine to what temperature should you cool the air? Assume that after removal of 50% of moisture from the air, the final air is saturated.
Air at 25 C and 750mmHg has a dew point of 16C. If you want to...
Air at 25 C and 750mmHg has a dew point of 16C. If you want to remove 50% of the initial moisture in the air (at a constant pressure of 750 mmHg), to what temperature should you cool the air?
A gas turbine expands air adiabatically at 1000 kPa and 550 ⁰C to 120 kPa and...
A gas turbine expands air adiabatically at 1000 kPa and 550 ⁰C to 120 kPa and 130⁰C. Air enters the turbine through a 0.25 m 2 opening with an aveage velocity of 45 m/s, and exhausts through a 1 m2 opening. Assume the air is ideal gas with constant specific heats. Take the constant pressure specific heat and gas constant of air as Cp= 1.05 kJ/(kg K) and R=0.287 kJ/(kg K), respectively. Determine; (a) the mass flow rate of air...
Air entering a dryer has a temperature (dry bulb) of 60°C and a dew point of...
Air entering a dryer has a temperature (dry bulb) of 60°C and a dew point of 26.7°C. Using the humidity chart, determine the actual humidity H, percentage humidity HP, humid heat cS and humid volume vH.
There are 10 m3/s of moist air at 22C and relative humidity of 50% that enter...
There are 10 m3/s of moist air at 22C and relative humidity of 50% that enter a heating element until its temperature becomes 35C. Determine the amount of heat required and the final %Rh of the air.
Air enters a counter-flow drier at 70˚C dry bulb temperature and 20˚C dew point temperature. Air...
Air enters a counter-flow drier at 70˚C dry bulb temperature and 20˚C dew point temperature. Air leaves the drier at 40˚C and 60% relative humidity. The initial moisture content of the product is 82% (wet basis). The amount of air moving through the drier is 2000kg of dry air per hour. The mass flow rate of the product is 10kg dry solid per hour. What is the final moisture content of the dried product in wet basis?
Air enters a counter-flow drier at 70˚C dry bulb temperature and 20˚C dew point temperature. Air...
Air enters a counter-flow drier at 70˚C dry bulb temperature and 20˚C dew point temperature. Air leaves the drier at 40˚C and 60% relative humidity. The initial moisture content of the product is 82% (wet basis). The amount of air moving through the drier is 2000kg of dry air per hour. The mass flow rate of the product is 10kg dry solid per hour. What is the final moisture content of the dried product in wet basis?
A8. For air with temperature and dew-point values given below in °C, find the LCL value...
A8. For air with temperature and dew-point values given below in °C, find the LCL value (km). T, Td T, Td a. 15, 12 g. 5, 4 b. 15, 10 h. 5, 0 c. 15, 8 i. 5, –5
Air enters the compressor at 100 kPa, 300 K and is compressed to 1000 kPa. The...
Air enters the compressor at 100 kPa, 300 K and is compressed to 1000 kPa. The temperature at the inlet to the first turbine stage is 1400 K. The expansion takes place isentropically in two stages, with reheat to 1400 K between the stages at a constant pressure of 300 kPa. A regenerator having an effectiveness of 100% is also incorporated into the cycle. The turbine and the compressor each have am isentropic efficiency of 80%. Determine the following: (a.)...
air at 110 kpa and 25 degrees C enters a diffuser with diameter of 10 cm...
air at 110 kpa and 25 degrees C enters a diffuser with diameter of 10 cm and 25 cm at entrance and exit. if the velocity of air at the entrance is 15 m/s and leaving the diffuser at 1.5 m/s. determine a.) mass rate of air b.) density of air at the exit