Ultrasonic level transmitter, which performs calculations to
convert the distance of wave travel into a measure of level in the
tank. The time lapse between firing the sound burst and receiving
the return echo is directly proportional to the distance between
the transducer and the material in the vessel. The medium is
normally air over the material’s surface but it could be a blanket
of some other gases or vapours. The instrument measures the time
for the bursts to travel down to the reflecting surface and return.
This time will be proportional to the distance from the transducer
to the surface and can be used to determine the level of fluid in
the tank. This basic principle lies at the heart of the ultrasonic
measurement technology and is illustrated in the equation: Distance
= (Velocity of Sound x Time)/2. These noncontact devices are
available in models that can convert readings into 4–20 mA outputs
to DCSs, PLCs, or other remote systems.
The frequency range for ultrasonic methods is in the range of
15…200 kHz. The lower frequency instruments are used for more
difficult applications; such as longer distances and solid level
measurements and those with higher frequency are used for shorter
liquid level measurements.
For practical applications of ultrasonic measurement method, a
number of factors must be considered. A few key points are:
- The speed of sound through the medium (usually air) varies with
the medium’s temperature. The transducer may contain a temperature
sensor to compensate for changes in operating temperature that
would alter the speed of sound and hence the distance calculation
that determines an accurate level measurement. Temperature
compensation is provided to account for uniform temperature
variances of the sound medium. The temperature sensor is placed
inside the transducer and the signal is sent to the transceiver via
the transducer’s wiring. Optionally, an alternate temperature
sensor can be used to provide a temperature input, rather than by
using the integral temperature sensor. If the temperature of the
sound medium is to remain constant, instead of using either the
integral temperature compensation or the remote sensor, the desired
temperature may be entered during the transceiver
configuration.
- The presence of heavy foam/dust on the surface of the material
can act as a sound absorbent. In some cases, the absorption may be
sufficient to preclude use of the ultrasonic technique. To enhance
performance where foam/dust or other factors affect the wave travel
to and from the liquid surface, some models can have a beam guide
attached to the transducer.
- Extreme turbulence of the liquid can cause fluctuating
readings. Use of a damping adjustment in the instrument or a
response delay may help overcome this problem. The transceiver
provides damping to control the maximum changing rate of the
displayed material level and fluctuation of the mA output signal.
Damping slows down the rate of response of the display especially
when liquid surfaces are in agitation or material falls into the
sound path during filling