In the reactor safety study, the failure rate of a diesel generator can be described as having a lognormal distribution with the upper and lower 90 % bounds of 3x10^-2 and 3x10^-4, respectively. a) Determine prior distribution in lognormal distribution. b) The given nuclear plant experiences 2 failures in 8,760 hours of operation. Determine the posterior distribution based on Poisson distribution. c) Determine the upper and lower 90 % bounds given this plant experience. (Consider the reactor safety study values as prior information.

Solutions

Expert Solution

a)

Consider a random variable X that describes the failure rate of the diesel generator

Given that X has a lognormal distribution, the random variable Y given as Y = ln(X) will have a normal distribution

For the upper 90% boundary as 0.03,

Y1 = ln (0.03) = -3.5

For the lower 90% boundary as 0.0003,

Y2 = ln (0.0003) = -8.11

Mean of the normal distribution E(Y) = (-3.5 – 8.11)/2 = -5.80

The corresponding value of X = eY = e(-5.80) = 0.003

Y1 = E(Y) + σY z

Using z tables, for 90% confidence interval z = 1.64

Substituting in the above equation for Y1

-3.5 = -5.8 + 1.64σY

σY = 1.399

The log normal distribution is given as:

ln (X) ~ N (-5.80, 1.3992)

b)

Given a Poisson Distribution, the Probability of the random variable for the number of failures in a Poisson distribution is given as:

P(X = x) = e − λ λx / x!

Mean of the Poisson Distribution = λ = average number of failures = 2 failures/year

Thus the Poisson’s distribution is given as

P(X = x) = e −2 2x / x!

c)

90% confidence interval for the Poisson’s distribution is given as:

λ± 1.64 * sqrt (λ)

  • 2 ± 1.64* sqrt(2)
  • [ -0.32 , 4.32 ]

Related Solutions

Diesel Generator A I MVA diesel three-phase generator is rated at 4.16 kV, 60 Hz, and...
Diesel Generator A I MVA diesel three-phase generator is rated at 4.16 kV, 60 Hz, and connected as Y its neutral is kept floating. It is directly tied to three loads, one consuming 50% of its capacity, and each of the other two consuming 25% of its capacity. A three-phase to ground fault could occur at any of the loads. Draw a one-line diagram of this system, then describe what type of faults could occur in the generator and diesel...
ABC Company wants to buy diesel generator at a price of $1,600,000,000 . The alternatives are...
ABC Company wants to buy diesel generator at a price of $1,600,000,000 . The alternatives are as follows: -Buy cash at a price of $1,600,000,000 OR -Rent at a price of $30,000,000 per month. Assumption of a deposit interest of 7% a year. In your opinion, which one to choose ?
One generator is placed in standby redundancy to the main generator. The faliure rate of each...
One generator is placed in standby redundancy to the main generator. The faliure rate of each generator is estimated to be λ = 0.05/hr. Compute the reliability of the system for 10 hrs and its MTBF assuming that the sensing and switching device is 100% reliable. If the reliability of this device is only 80%, how are the results modified?
What are the benefits described in the USP 800 safety updates?
What are the benefits described in the USP 800 safety updates?
An article presents a study of the failure pressures of roof panels. Following are the failure...
An article presents a study of the failure pressures of roof panels. Following are the failure pressures, in kPa, for five panels constructed with 6d smooth shank nails. These data are consistent with means and standard deviations presented in the article. 3.32 2.52 3.45 2.38 3.01 Find a 95% confidence interval for the mean failure pressure for this type of roof panel. Round the answers to three decimal places. The 95% confidence interval is ( , ).
A hospital has three emergency generators for use in case of a power failure. Each generator...
A hospital has three emergency generators for use in case of a power failure. Each generator functions independently, and the manufacturer claims that the probability that each generator will function properly during a power failure is 0.95. 1. List all of the possible outcomes in the sample space, S, and find the probability associated with each outcome. 2. Define the random variable X = the number of generators that fail. Calculate the value of X for each outcome in the...
A steam generator is needed in the design of new mini-power plant. This generator can be...
A steam generator is needed in the design of new mini-power plant. This generator can be purchased with two different specification proposals, A or B. Proposal A has life of 15 years, a first cost of RM45,000 to buy with estimated an annual saving of RM3,500 per year and estimated for an annual operating & maintenance cost of RM750 per year. A salvage value of RM10,700 and one-off overhaul in year 9 that cost RM 1,500. Proposal B has a...
Which model, exponential failure rate or Weibull failure rate is suitable to capture the wearout process...
Which model, exponential failure rate or Weibull failure rate is suitable to capture the wearout process of a pump bearing? (justify). Using MS Excel and simulated data, estimate the reliability a pump bearing for every month over 10 years of operations (upload the MS Excel file on the D2L along with your answer sheet).
1. In a typical CANDU reactor, how many different ways can one control the reactor power?...
1. In a typical CANDU reactor, how many different ways can one control the reactor power? Describe the situations when each of these techniques are used?
What is the likely scenario that will happen if the Oxygen Transfer Rate in the reactor...
What is the likely scenario that will happen if the Oxygen Transfer Rate in the reactor is smaller than the Oxygen Uptake Rate (e.g. what will happen to your cells, doubling time and so on)?
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT