A number of piers of a reinforced concrete marine jetty which was constructed fifteen (15) years...

A number of piers of a reinforced concrete marine jetty which was constructed fifteen (15) years
ago are reported to undergo corrosion of reinforcement and in need of urgent repair. From an
investigation that has been performed on the affected piers, it has been suggested that up to
about 50 mm of the concrete cover have to be removed and replaced due to the presence of high
chloride content. Physical measurement on some of the badly corroded reinforcements suggests
that some rebars have experienced greater than 25 % lost in cross-sectional area. Suggest a
suitable retrofitting scheme and detail the work including the steps to be undertaken in
rehabilitating the affected piers so that the corrosion problem is arrested and the load carrying
capacity of the piers are restored. Provide appropriate sketches to aid your explanation.

Solutions

Expert Solution

RETROFITTING & REHABILITATION WORK STEPS FOR CROSSONED MARINE RCC PIER:-

There are three major techniques for strengthening reinforced concrete columns which are discussed below:

1. Reinforced Concrete Jacketing

It is one of the techniques used to improve or restore capacity of reinforced concrete column. The size of the jacket and the number and diameter of the steel bars used in the jacketing process depend on the structural analysis that was made to the column.

Reinforced Concrete Jacketing Process

  1. Initially, reduce or eliminate loads on columns temporarily if it is required. This is done by putting mechanical jacks and additional props between floors.
  2. After that, if it is found out that reinforcements are corroded, the remove the concrete cover and clean the steel bars using a wire brush or sand compressor.
  3. Then, coat the steel bars with an epoxy material that would prevent corrosion.
  4. If reducing loads and cleaning reinforcement is not needed, the jacketing process begin by adding steel connectors into the existing column.
  5. The steel connectors are added into the column by making holes 3-4mm larger than the diameter of the used steel connectors and 10-15cm depth.
  6. The spacing of new stirrups of the jacket in both the vertical and horizontal directions should not be more than 50cm.
  7. Filling the holes with an appropriate epoxy material then inserting the connectors into the holes.
  8. Adding vertical steel connectors to fasten the vertical steel bars of the jacket following the same procedure in step 5 and 6.
  9. Installing the new vertical steel bars and stirrups of the jacket according to the designed dimensions and diameters.
  10. Coating the existing column with an appropriate epoxy material that would guarantee the bond between the old and new concrete.
  11. Pouring the concrete of the jacket before the epoxy material dries. The concrete used should be of low shrinkage and consists of small aggregates, sand, cement and additional materials to prevent shrinkage. Steps of reinforced concrete jacketing are illustrated in Fig. 12. Steel Jacketing

    This technique is chosen when the loads applied to the column will be increased, and at the same time, increasing the cross sectional area of the column is not permitted.

    Steel Jacketing Process:-

  12. Removing the concrete cover.

  13. Cleaning the reinforcement steel bars using a wire brush or a sand compressor.
  14. Coating the steel bars with an epoxy material that would prevent corrosion.
  15. Installing the steel jacket with the required size and thickness, according to the design, and making openings to pour through them the epoxy material that would guarantee the needed bond between the concrete column and the steel jacket.
  16. Filling the space between the concrete column and the steel jacket with an appropriate epoxy material.In some cases, where the column is needed to carry bending moment and transfer it successfully through the floors, one should install a steel collar at the neck of the column by means of bolts or a suitable bonding material.

    3. FRP Confining or Jacketing

    For detailed description and design of strengthening reinforced concrete columns using FRP confining.


Related Solutions

reinforced concrete structure the roles of concrete and steel.
reinforced concrete structure the roles of concrete and steel.
Reinforced Concrete – concept and conditions to be fulfilled.
Reinforced Concrete – concept and conditions to be fulfilled.
What are the advantages of reinforced concrete beams compared with plain concrete beams?
What are the advantages of reinforced concrete beams compared with plain concrete beams?
A reinforced concrete beam of normal weight concrete with an effective depth of 20 IN and...
A reinforced concrete beam of normal weight concrete with an effective depth of 20 IN and a width of 12 IN is reinforced with 3 IN2 of grade 60 (fy = 60 KSI) rebar. The beam has a concrete compressive strength f’c of 3000 PSI. (a) Determine the maximum ultimate moment which can be applied to the beam. (b) If the only dead load on the beam is self-weight, determine the allowable uniformly distributed live load which can be applied...
Design a concrete mix for reinforced concrete beams of a structure. The structure is located in...
Design a concrete mix for reinforced concrete beams of a structure. The structure is located in a locality wherein water has excess of chlorides in it. Required average compressive strength of concrete has been determined to be 4700 psi. Beams have cross-section of 9 in. x 21 in. reinforced with 4 # 6 bars. Reinforcement has a concrete cover of 1.25 in. and there is a clear space of 1.0 in. between form surface and steel bars. Fine aggregate has...
I mention everything in detail (Concrete mix design) INTRODUCTION TO REINFORCED CONCRETE
I mention everything in detail (Concrete mix design) INTRODUCTION TO REINFORCED CONCRETE
Why structural concrete is reinforced by steel? Discuss the weakness and strength of both concrete and...
Why structural concrete is reinforced by steel? Discuss the weakness and strength of both concrete and steel in this case
Performance of Reinforced Concrete Slab due to Reinforcement Corrosion
Performance of Reinforced Concrete Slab due to Reinforcement Corrosion
Describe the mechanism of failure of Reinforced Concrete beam in bending        
Describe the mechanism of failure of Reinforced Concrete beam in bending        
Design a plain concrete footing for a 400 mm reinforced concrete wall that supports a DL...
Design a plain concrete footing for a 400 mm reinforced concrete wall that supports a DL = 185 KN/m and 95 KN/m live load. The base of the footing is to be 1.2 m below the final grade. fc’ = 20.7 Mpa and allowable soil pressure is 200 Kpa, weight of soil is 15.82 KN/m3. (ACI)
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT