Ex if std no: 1abcde, 161667 (a=6, b=1, c=6, d=6,
e=7)
In my case std 174702
Q1) Design a concrete mixture proportions which will be used for
offshore concrete platform. Norway is a world leader on offshore
concrete platforms with 1a of the world’s 30 larger offshore
concrete structures located on the Norwegian continental shelf. The
first of these platforms where the Ekofisk Tank installed in 1974
and the last was Troll gravity based structure installed in 1996.
The Sakhalin project is located in a harsh and artic environment
where concrete structures have proven excellent characteristics
with a minimum of maintenance. 80 mm slump value is required for
the Sakhalin project. 28-days concrete characteristic strength is
2b MPa. It is required that no more than 1 test result in 100 will
fall below the specified strength. The fine aggregate has a
fineness modulus of 2.60 and Zone 3. For Coarse Aggregate
(Uncrushed): SSD Bulk Specific Gravity: 2.65, Absorption Capacity:
2.b %, Total Moisture: 1.c % and Dry Rodded Unit Weight: 1345 kg/m3. For
Fine Aggregate (Uncrushed): SSD Bulk Specific Gravity: 2.70, Total
Moisture: 3.d % and Free Moisture: 2 %. Cement: Portland Composite
Cement, Specific Gravity: 2.97. For 0.e5 m3 of concrete, binder
amount is calculated as 120 kg (Use ACI Method of Mix
Design)
Ans) Let the total volume of trial mix be 1 m3 . The nominal aggregate size suitable for construction of concrete platform is 19 mm.According to ACI 211.1-91, table 6.3.3, for 80 mm slump and nominal aggregate size of 19 mm , amount of water required per cubic meter of concrete is 193 kg
=> Amount of water = 193 kg per m3 concrete
Since, concrete exposed to aggressive environment, class of exposure is severe, so air content for 19 mm aggregate size is 6 %
Now, required compressive strength as per ACI,
fcr = f'c + 8.3
=> fcr = 24 + 8.3 = 32.3 MPa
Now according to Table 6.3.4 (a) , for compressive strength of 32.3 MPa, water cement ratio is 0.43
Minimum Cement content per cubic meter concrete = 120 / 0.95 = 480 kg
Hence, amount of cement = Amount of water / w-c ratio = 193/ 0.43 = 448.84 kg < 480 kg
Hence. provide minimum cement content = 480 kg/
Now, according to table 6.3.6 for nominal aggregate size of 19 mm and fineness modulus of 2.60 , volume of coarse aggregate is 0.64 m3
=> Amount of coarse aggregate = dry rodded density x volume = 1345 x 0.64 = 860.8 kg
Volume of fine aggregate = Total volume of concrete - Volume of all water, cement, coarse aggregate and air
=> Fine aggregate volume = 1 - [(193/1000) + (480 / 2.97 x 1000) + (860.8/ 2.65 x 1000) + 0.06]
=> Fine aggregate volume = 1 - 0.74 = 0.26 m3
=> Amount of fine aggregate = volume x specific gravity x water density = 0.26 x 2.7 x 1000 = 702 kg
Now, since both aggregates has moisture and has absorption capacity , amount of mixing water needs to be corrected as shown :
Net Water absorbed by coarse aggregate = (0.017 - 0.024) x 860.80 = -6.03 kg
Net Water absorbed by fine aggregate = (0 - 0.05) x 702 = -35.1 kg
=> Actual amount of water to be added = 193 - 6.03 - 35.1 = 151.87 kg
Hence, batch weight for trial mix of 1 cubic meter is as follows :
Material | Amount (kg) |
Cement | 480 |
Water | 151.87 |
Fine aggregate | 702 |
Coarse aggregate | 860.8 |