The type of 3 phase induction motor which uses a squirrel cage
rotor is called squirrel cage induction motor.
All induction motors have a rotor and a stator. Basically, it is
the construction of rotor which makes Squirrel Cage Induction Motor
different from Wound Type Induction Motor. Stator is same in both
types of motors.
A squirrel cage induction motor generally operates at a constant
speed. This speed is near to synchronous speed.
Starting in-rush current in squirrel cage motors is controlled
by applying reduced voltage to the stator. These methods are
sometimes called as reduced voltage methods for starting of
squirrel cage induction motors. For this purpose, following methods
are used:
- By using primary resistors
- Autotransformer
- Star-delta switches
- The purpose of primary resistors is to drop some voltage and
apply a reduced voltage to the stator. Consider, the starting
voltage is reduced by 50%. Then according to the Ohm's law (V=I/Z),
the starting current will also be reduced by the same percentage.
From the torque equation of a three phase induction motor, the
starting torque is approximately proportional to the square of the
applied voltage. That means, if the applied voltage is 50% of the
rated value, the starting torque will be only 25% of its normal
voltage value. This method is generally used for a smooth
starting of small induction motors. It is not recommended
to use primary resistors type of starting method for motors with
high starting torque requirements.
Resistors are generally selected so that 70% of the rated voltage
can be applied to the motor. At the time of starting, full
resistance is connected in the series with the stator winding and
it is gradually decreased as the motor speeds up. When the motor
reaches an appropriate speed, the resistances are disconnected from
the circuit and the stator phases are directly connected to the
supply lines
- Auto-transformers are also known as auto-starters. They can be
used for both star connected or delta connected squirrel cage
motors. It is basically a three phase step down transformer with
different taps provided that permit the user to start the motor at,
say, 50%, 65% or 80% of line voltage. With auto-transformer
starting, the current drawn from supply line is always less than
the motor current by an amount equal to the transformation ratio.
For example, when a motor is started on a 65% tap, the applied
voltage to the motor will be 65% of the line voltage and the
applied current will be 65% of the line voltage starting value,
while the line current will be 65% of 65% (i.e. 42%) of the line
voltage starting value. This difference between the line current
and the motor current is due to transformer action. The internal
connections of an auto-starter are as shown in the figure. At
starting, switch is at "start" position, and a reduced voltage
(which is selected using a tap) is applied across the stator. When
the motor gathers an appropriate speed, say upto 80% of its rated
speed, the auto-transformer automatically gets disconnected from
the circuit as the switch goes to "run" position.
The switch changing the connection from start to run position may
be air-break (small motors) or oil-immersed (large motors) type.
There are also provisions for no-voltage and overload, with time
delay circuits on an autostarter.
- This method is used in the motors, which are designed to run on
delta connected stator. A two way switch is used to connect the
stator winding in star while starting and in delta while running at
normal speed. When the stator winding is star connected, voltage
over each phase in motor will be reduced by a factor 1/(sqrt. 3) of
that would be for delta connected winding. The starting torque will
1/3 times that it will be for delta connected winding. Hence a
star-delta starter is equivalent to an auto-transformer of ratio
1/(sqrt. 3) or 58% reduced voltage...
No motor for twice the rated torque is
not recommended because operating the motor at half of torque will
lead to decrease in efficiency and low power factor