the reinforced concrete tied column that is part of braced frame sized to the dimensions 375mm...

the reinforced concrete tied column that is part of braced frame sized to the dimensions 375mm by 300mm .the column carries vertical ultimate load Pu=490kN (dead load only PD=134kN) and ultimate moment about strong axis Mu=110kN at top and Mu=117kN at bottom bent column in single curvature. if the clear height of the column Lu=4.80m k=0.83f'c=28MPa and fy=420 MPa , determine the reinforcement required

Solutions

Expert Solution

Solution:- the values given in the question are as follows:

size of column=375 mm * 300 mm

vertical ultimate load(Pu)=490 KN, (dead load=134 KN)

moment about strong axis(Mut) at top=110 KN

moment about strong axis(Mub) at bottom=117 KN

clear height of column(L)=4.8 m

effective length(Leff)=K*L=0.8*4.8=3.84 m (where, k=0.8)

fIc=28 MPa & fy=420 MPa

Calculation reinforcement required in column:

using limit state(LSM) of method

assume short column with small eccentricity loaded column (e=very less eccentricity 0.05*dimension of column)

ultimate load(Pu)=0.4fIc*Ac+0.75As*fy [Eq-1]

where, Ac=conrete area

As=steel area(reinforcement area)

Ac=gross area-As (gross area=cross-sectional area of column)

Ac=300*375-As

Ac=112500-As mm^2

values put in equation-1

490*10^3=0.4*28*(112500-As)+0.75*As*420 [where, Pu=490*10^3 N ,fy=420 N/mm^2 and fIc=28 N/mm^2 ]

490*10^3=126*10^4-11.2As+315As

490*10^3=126*10^4+303.8As

303.8As=490*10^3-126*10^4=-770000

As=-770000/303.8=-2534.56 mm^2 [area of inforcement not in negative, so negative value taken as positive value]

As=2534.56 mm^2

check the area of reinforcement

minumum area of reinforcement in column according to ACI

Asmin=0.8%of total cross-section area of column

Asmin=(0.8/100)*300*375=900 mm^2

As>Asmin [so the design reinforcement is safe]

let provide 20 mm diameter main bar

number of bar(n)= As/cross-section area of one bar =2534.56/{(3.14/4)*20^2}

number of bar(n)=8.07=8 bars

number of bars(n)=8

ties(stirrups bar)

minimum dia of ties=(3/8)*20=7.5 mm

provide dia of lateral ties=8 mm

spacing of lateral ties=MInimum of{leat lateral dimension of column, 16*dia of main bar, 300 mm}

spacing of lateral ties=MInimum of{300mm , 16*20=320 mm , 300 mm}

spacing of lateral ties= 300 mm

[Ans]


Related Solutions

Find the required rectangular cross-sectional area for a tied reinforced concrete column which should support a...
Find the required rectangular cross-sectional area for a tied reinforced concrete column which should support a load of 300 tons. Use 4000 psi concrete, ultimate steel stress of 60,000 psi and 4% steel.
Design a square concrete column footing to support a 500-mm x 500-mm reinforced concrete column. The...
Design a square concrete column footing to support a 500-mm x 500-mm reinforced concrete column. The center of the column and footing must coincide. Loads: ???=350 ??, ???=480 ??, ???=100 ??−?, ???=130 ??−? Column Design Criteria: ??′=28 ???, ??=400??? Footing Design Criteria: ??′=28 ???, ??=400???, ??=175 ???,??=1.50 ?, ??=16 ??/?3,??=24 ??/?3, ??=20 ??, assume a thickness of the footing of 500 mm.
Design a square concrete column footing to support a 400-mm x 400-mm reinforced concrete column. The...
Design a square concrete column footing to support a 400-mm x 400-mm reinforced concrete column. The center of the column and footing must coincide. Loads: ???=350 ??, ???=480 ??, ???=100 ??−?, ???=130 ??−? Column Design Criteria: ??′=28 ???, ??=400??? Footing Design Criteria: ??′=28 ???, ??=400???, ??=180 ???,??=1.70 ?, ??=16 ??/?3,??=24 ??/?3, ??=25 ??, assume a thickness of the footing of 700 mm.
A short reinforced concrete column is subjected to a 1000 kN axial compressive load. The moduli...
A short reinforced concrete column is subjected to a 1000 kN axial compressive load. The moduli of elasticity of plain concrete and steel are 25 GPa and 207 GPa, respectively, and the cross-sectional area of steel is 2% of that of the reinforced concrete. Considering the column as a structural member made of a composite material and subjected to load parallel to the steel rebars, calculate the following: a. the modulus of elasticity of the reinforced concrete b. the load...
A short reinforced concrete column is subjected to a 1000 kN axial compressive load. The moduli...
A short reinforced concrete column is subjected to a 1000 kN axial compressive load. The moduli of elasticity of plain concrete and steel are 25 GPa and 207 GPa, respectively, and the cross-sectional area of steel is 2% of that of the reinforced concrete. Considering the column as a structural member made of a composite material and subjected to load parallel to the steel rebars, calculate the following: a. the modulus of elasticity of the reinforced concrete b. the load...
Please answer the question: A 24 inch diameter spirally reinforced concrete column with a 1.5 inch...
Please answer the question: A 24 inch diameter spirally reinforced concrete column with a 1.5 inch cover to the spiral is reinforced with Grade 60 bars and has a concrete compressive strength of 5,000 psi. Determine the required diameter and pitch of the spiral reinforcement.
reinforced concrete structure the roles of concrete and steel.
reinforced concrete structure the roles of concrete and steel.
Design a reinforced concrete steel rectangular tie column with ACI standards, total LL = 14.0625 kips,...
Design a reinforced concrete steel rectangular tie column with ACI standards, total LL = 14.0625 kips, total DL = 18.95625kips, cross-section 12in by 12 in, Hight of column 12ft. Show all the steps and which table used. Assume the information which is not given with justifications. Show drawing as well. If the high is not suitable you can change it.
Reinforced Concrete – concept and conditions to be fulfilled.
Reinforced Concrete – concept and conditions to be fulfilled.
What are the advantages of reinforced concrete beams compared with plain concrete beams?
What are the advantages of reinforced concrete beams compared with plain concrete beams?
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT