Question

In: Civil Engineering

Design a reinforced concrete steel rectangular tie column with ACI standards, total LL = 14.0625 kips,...

Design a reinforced concrete steel rectangular tie column with ACI standards, total LL = 14.0625 kips, total DL = 18.95625kips, cross-section 12in by 12 in, Hight of column 12ft. Show all the steps and which table used. Assume the information which is not given with justifications. Show drawing as well. If the high is not suitable you can change it.

Solutions

Expert Solution

Solution:- the values given in the question are as follows:

dead load(DL)=14.0625 kips

live load(LL)=18.95625 kips

cross-section of column=12 in*12 in

length of column(L)=12 ft

let we use the grade of concrete is C28 and S420

characteristic strength of concrete(fIc)=4000 psi

yield strength of steel(fy)=60000 psi

slenderness ratio()=k*Lu/(leat lateral dimension)

where, k=1.0

Lu=12 ft =12*12 in

least lateral dimension=12 in

slenderness ratio()=(12*12)/12=12

slenderness ratio()=12 40 ,so the column is short column.

let we design axially(with minimum eccentricity) loaded short column

load carrying capacity of column(Pu)=0.4*fc*Ac+0.75*fy*As

where, Ac=coss-section area of concrete

As=cross-section area of steel

Ac=Ag-As

gross area(Ag)=12*12=144 in^2

Ac=144-As

load carrying capacity of column(Pu)=0.4*4000*(144-As)+0.75*60000*As , [Eq-1]

total load on column(P)=DL+LL

total load on column(P)=18.95625+14.0625

total load on column(P)=33.58125 kips

total load on column(P)=33.58125*10^3 lb

we design the column for load P

Pu=P , put in above equation-(1)

33.58125*10^3=230400-1600As+45000As

33581.25-230400=43400As

As=-196818.75/43400 in^2

According to above equation, area of steel goes in negative, but area of steel in column never goes in negative.

so we will provide area of steel greater than the minimum area of steel needed for this column.

area of steel(As)=2% of gross area

area of steel(As)=(/100)*144

area of steel(As)=2.88 in^2

provide 0.875 in diameter steel bar into the column.

number of bars(n)=As/area of single bar

area of single bar=(Pi/4)*0.875^2

area of single bar=(3.14/4)*0.875^2

area of single bar=0.6013 in^2

number of bars(n)=2.88/0.6013=4.789 5

provide 0.875 in diameter of 6 bars.

let provide 0.375 in diameter tie bars

spacing of tie bars=minimum of {B or D , 16 , 11.81 in}

spacing of tie bars=minimum of {12 in , 16*0.875=14 , 11.81 in}

spacing of tie bars=11.81 in

provide spacing of tie bars is 11 in center to center.

let provide 1 in constant clear cover, shown in figure.

[Ans]


Related Solutions

Design a rectangular reinforced concrete beam to resist a total design moment Mu=400 ft.kips (this includes...
Design a rectangular reinforced concrete beam to resist a total design moment Mu=400 ft.kips (this includes the moment due to beam weight). Architectural considerations require that the width (b) be 18 in. and the overall depth (h) be 26 in. Use f′c=4,000 psi and fy=60,000 psi. Sketch your design.
Design a square concrete column footing to support a 500-mm x 500-mm reinforced concrete column. The...
Design a square concrete column footing to support a 500-mm x 500-mm reinforced concrete column. The center of the column and footing must coincide. Loads: ???=350 ??, ???=480 ??, ???=100 ??−?, ???=130 ??−? Column Design Criteria: ??′=28 ???, ??=400??? Footing Design Criteria: ??′=28 ???, ??=400???, ??=175 ???,??=1.50 ?, ??=16 ??/?3,??=24 ??/?3, ??=20 ??, assume a thickness of the footing of 500 mm.
Design a square concrete column footing to support a 400-mm x 400-mm reinforced concrete column. The...
Design a square concrete column footing to support a 400-mm x 400-mm reinforced concrete column. The center of the column and footing must coincide. Loads: ???=350 ??, ???=480 ??, ???=100 ??−?, ???=130 ??−? Column Design Criteria: ??′=28 ???, ??=400??? Footing Design Criteria: ??′=28 ???, ??=400???, ??=180 ???,??=1.70 ?, ??=16 ??/?3,??=24 ??/?3, ??=25 ??, assume a thickness of the footing of 700 mm.
reinforced concrete structure the roles of concrete and steel.
reinforced concrete structure the roles of concrete and steel.
Design a concrete mix using ACI Method required for an exterior column to be located above...
Design a concrete mix using ACI Method required for an exterior column to be located above ground level in an area where it will be wet and subjected to substantial freezing and thawing. The concrete is required to have an average 28-day compressive strength of 30 MPa. For the conditions of placement, the slump should be between 25 and 100 mm. The column is 300 mm square with a minimum clear space for aggregate of 50 mm. The properties of...
Find the required rectangular cross-sectional area for a tied reinforced concrete column which should support a...
Find the required rectangular cross-sectional area for a tied reinforced concrete column which should support a load of 300 tons. Use 4000 psi concrete, ultimate steel stress of 60,000 psi and 4% steel.
Design a rectangular reinforced concrete beam for a simple span of 35 ft. Uniform service loads...
Design a rectangular reinforced concrete beam for a simple span of 35 ft. Uniform service loads are 1.0 kip/ft dead load (excluding the self-weight of the beam) and 1.2 kips/ft live load. Use f′c=4,000 psi and fy=60,000 psi. Sketch your design.
Design a rectangular reinforced concrete beam for a simple span of 32 ft. Uniform service loads...
Design a rectangular reinforced concrete beam for a simple span of 32 ft. Uniform service loads are 1.5 kips/ft dead load and 2.0 kips/ft live load. Assuming that the total depth h is not to exceed 32 in. and that there is no limitation on the width b. Use f′c = 3000 psi and fy = 60,000 psi. Sketch your design
W shape column must support a axial load (DL=500 kips y LL= 300 kips). The element...
W shape column must support a axial load (DL=500 kips y LL= 300 kips). The element is 30 ft length and braced in the y direction at 14 ft from the column base. The end support conditions are (fixed/pinned). Justify the material’s selection. verify slenderness and local buckling and Select the lightest section
Why structural concrete is reinforced by steel? Discuss the weakness and strength of both concrete and...
Why structural concrete is reinforced by steel? Discuss the weakness and strength of both concrete and steel in this case
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT