A counter-flow double-pipe heat exchanger is to heat water from 20ºC to 80ºC at a rate...

A counter-flow double-pipe heat exchanger is to heat water from 20ºC to 80ºC at a rate of 1.2 kg/s. The heating is to be accomplished by geothermal water available at 160ºC at a mass flow rate of 2 kg/s. The inner tube is thin-walled, and has a diameter of 1.5 cm. If the overall heat transfer coefficient of the heat exchanger is 640 W/(m2.ºC), determine the length of the heat exchanger required to achieve the desired heating using the effectiveness-NTU method. Take the specific heat of geothermal water to be 4.31 kJ/(kg.ºC) and that of water to be 4.18 kJ/(kg.ºC).

Solutions

Expert Solution

Here the cold fluid (denoted as subscript c) is water and hot fluid (denoted as subscript h) is geothermal water.

Given: Initial and final temperature of water respectively, t1= 200C and t2= 800C

Mass flow rate of water, c=1.2 kg/s

Initial temperature of geothermal water, T1=1600C

Mass flow rate of geothermal water, h=2 kg/s

Overall heat transfer coefficient, U= 640 W/m20C

Diameter of the tube, D=1.5 cm= 0.015 m

Specific heat of geothermal water, Cph=4.31 kJ/kg0C

Specific heat of water, Cpc=4.18 kJ/kg0C

Step 1: Determine the heat capacity flow rate of hot and cold fluid to get the minimum value of specific heat flow rate.

Heat capacity flow rate of hot fluid, Ch is Ch= hCph

Ch= 2 kg/s*4.31 kJ/kg0C=8.62 kJ/s0C

Ch= 8.62 kW/0C

Heat capacity flow rate of cold fluid, Cc is Cc= cCpc

Cc = 1.2 kg/s*4.18 kJ/kg0C= 5.016 kJ/s0C

Cc = 5.016 kW/0C

As Cc < Ch, the minimum and maximum value will be Cmin= 5.016 kW/0C and Cmax = 8.62 kW/0C respectively.

The capacity ratio, c=Cmin/Cmax= 5.016/8.62=0.5819=0.582

c = 0.582

Step 2: Calculate the maximum heat transfer rate and actual heat transfer rate.

Maximum heat transfer rate, is calculated using the expression

The actual heat transfer rate, is calculated using the expression

Step 3: Calculate Effectiveness of heat exchanger and NTU

The effectiveness of a heat exchanger is

  

For a counter flow double pipe heat exchanger, Number of Transfer Units, NTU is obtained from the effectiveness relation for heat exchanger

where c is the Capacity Ratio (Determined in earlier steps)

Step 4: Length of heat exchanger required to achieve the desired heating is

where L is the Length of the heat exchanger

D is the Diameter of the tube

As is the Heat Transfer Surface Area

As is obtained from the expression

Thus the length of the heat exchanger for the calculated heat transfer surface area is

Therefore, the length of heat exchanger required is L= 108.45 m which can be approximated to 109 m.


Related Solutions

A counter-flow double-pipe heat exchanger is heating water from 20 to 80 C at a rate...
A counter-flow double-pipe heat exchanger is heating water from 20 to 80 C at a rate of 1.2 kg/s. The heating is provided by water at 160 C and a rate of 2 kg/s. The inner tube has a diameter of 1.5 cm, and the U is 640 W/m2 K. Use the effectiveness-NTU method to determine the length of the heat exchanger required.
A double-pipe heat exchanger is designed as an engine oil cooler. The flow rate of oil...
A double-pipe heat exchanger is designed as an engine oil cooler. The flow rate of oil is 5 kg/s, and it will be cooled from 60°C to 40°C through annulus (ID = 0.10226 m, OD = 0.1143 m). Sea water flows through the tubes (ID = 0.02664 m, OD = 0.03340 m) and is heated from 10°C to 30°C. The number of bare tubes in the annulus is 3, and the length of the hairpin is 3 m. Assume that...
A double-pipe heat exchanger operating in counter current mode is to heat a fluid(Cp 1.7 kJ/kg...
A double-pipe heat exchanger operating in counter current mode is to heat a fluid(Cp 1.7 kJ/kg K) from 50°C to 95°C at a rate of 4.5 kg/s. The heating is to be accomplished by hot fluid (Cp=1.97 kJ/kg K) available at 200°C at a mass flow rate of 6 kg/s. The inner tube is thin-walled and has a diameter of 4 cm. If the overall heat transfer coefficient of the heat exchanger is 680 W/m2 °C, determine the length of...
A double-pipe heat exchanger is used to condense steam at 40°C saturation temperature. Water at an...
A double-pipe heat exchanger is used to condense steam at 40°C saturation temperature. Water at an average bulk temperature of 20°C flows at 2 m/s through the inner tube (copper, 2.54 cm ID, 3.05 cm OD). Steam at its saturation temperature flows in the annulus formed between the outer surface of the inner tube and outer tube of 6 cm ID. The average heat transfer coefficient of the condensing steam is 6,000 W/m2 ? K, and the thermal resistance of...
Water is used to cool ethylene glycol in a 18.3-m-long double pipe heat exchanger made of...
Water is used to cool ethylene glycol in a 18.3-m-long double pipe heat exchanger made of 4-std and 2-std (both type M) copper tubing. The water inlet temperature is 15.6°C and the ethylene glycol inlet temperature is 82.2°C. The flow rate of the ethylene glycol is 9.07 kg/s, while that for the water is 13.6 kg/s. Calculate the expected outlet temperature of the ethylene glycol and determine the pressure drop expected for both streams. Assume counterflow, and place the ethylene...
HEAT TRANSFER: HEAT EXCHANGER Oil flows in a heat exchanger with a mass flow rate of...
HEAT TRANSFER: HEAT EXCHANGER Oil flows in a heat exchanger with a mass flow rate of 20 kg/s and is to be cooled from 175 to 65°C with water as a coolant flowing at a rate of 30 kg/s and an inlet temperature of 12°C. The overall heat transfer coefficient is U = 1250 W/m2⋅K. a) Sketch the temperature profile and calculate the mean temperature for parallel flow, counter flow, and cross flow heat exchangers.. b) Determine the area required...
A heat exchanger with one body and eight pipe passes is designed. Water flows from the...
A heat exchanger with one body and eight pipe passes is designed. Water flows from the exhaust gas pipes as cold fluid by the body as cold fluid. Exhaust gas to the system at 210 ° C and entering at a temperature of 140 ° C The heat transfer coefficient is 392 W / m2K. On the other hand, water enters 16 iron (k = 38 W / mK) pipes with an inner diameter and outer diameter of 32 mm...
A double pipe heat exchanger is to be designed to cool 5 gal/min of hot oil...
A double pipe heat exchanger is to be designed to cool 5 gal/min of hot oil from 250°F to 120°F using 10 gal/min of cooling water available at 70°F. The heat exchanger is to consist of sections of 0.75 inch 16 BWG copper tubing inside 1.5 inch 16 BWG tubing; the water flows in the annular space. The shell-side heat transfer coefficient for this system is known to be 737 Btu/hr×ft2×°F. a) Estimate the required length of the countercurrent exchanger,...
For the double-pipe heat exchanger of Problem 3.10, calculate the outlet temperatures of the two streams...
For the double-pipe heat exchanger of Problem 3.10, calculate the outlet temperatures of the two streams when the unit is first placed in service. Q:3.10 A hydrocarbon stream is to be cooled from 200◦F to 130◦F using 10,800 lb/h of water with a range of 75–125◦F. A double-pipe heat exchanger comprised of 25 ft long carbon steel hairpins will be used. The inner and outer pipes are 1.5- and 3.5-in. schedule 40, respectively. The hydrocarbon will flow through the inner...
A 10 ft long double pipe heat exchanger consisting of a 1 in sch 40 (1.315...
A 10 ft long double pipe heat exchanger consisting of a 1 in sch 40 (1.315 in OD, 1.029 in ID) inner pipe within a 4 in sch 40 (3.998 in ID) outer pipe uses chilled water to cool hot glycerin (the water flows in the annulus and glycerin in the inner pipe). The pipes are constructed of AISI 302 stainless steel. The mean velocities of the water and glycerin are 4 ft/s and 1.3 ft/s, respectively. If the average...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT