  1. (a) The air conditioning unit of a car is operating on a summer day when the temperature is 37°C. It cools the air to 6°C using 3kW of power output. The A/C has a COP of 4. Find the mass flow rate of the cold air that the A/C unit can provide on that particular day. (15 points)

  2. (b) A building freezer that is used to freeze vegetables requires 40 tons of refrigeration to keep the food frozen. The temperature of the freezer is -35°C and the ambient temperature outside the building is 30°C. If the performance of the freezer is 20% of the theoretical best possible cycle, what is the power required to run the freezer. 1 ton of refrigeration is equivalent to 210 kJ/min. (15 points

Solutions

Expert Solution

Part (a):

COP of refrigerator is defined as ratio of Net cooling effect produced to Work Supplied to System.

To determine mass flow rate of Air

mf= mass flow rate of water

C = Specific heat capacity of water at constant pressure = 1.00 kJ/kg

Mass flow rate = 2 Kg Per second.

(b) Refrigeration capacity required = 40 tons of refrigeration

We know 1 ton of refrigeration = 3.5 KJ/s

therefore 40 tons of refrigeration = 40*3.5 = 140 KJ/s

Best Thoretical COP will be, if Refrigeration system works on reverse carnot cycle

TL = -35 C = 238 K

TH = 30 C = 303 K

Working COP = 0.2* COPtheoretical

Working COP = 0.7323

Therefore


Related Solutions

Air enters an air conditioning unit at 32oC, 80% relative humidity, and with a mass flowrate...
Air enters an air conditioning unit at 32oC, 80% relative humidity, and with a mass flowrate of 12 kg/min. It is to be conditioned to 25oC and 50% relative humidity. In order to do this, part of the moisture in the air must be removed as condensate at 30oC. Be able to draw the path that the atmospheric air takes on the psychrometric chart. Find a. The rate of moisture removal from the air, mw  b. The rate of...
The flow rate of warm air into the air conditioning is 5,000 cfm. An air conditioning...
The flow rate of warm air into the air conditioning is 5,000 cfm. An air conditioning system takes outdoor air at 95 degrees F dry-bulb and 70% relative humidity, and discharges it at 60 degrees F dry-bulb and 95% relative humidity. The air conditioning system operates on a vapor compression cycle using R134a between 20 and 200 psia. Refrigerant enters the compressor at 20 degrees F and leaves the compressor at 180 degrees F. Refrigerant enters the evaporator coil at...
A central air conditioning unit was installed at an initial cost of $65,000 and was expected...
A central air conditioning unit was installed at an initial cost of $65,000 and was expected to have a salvage value of $5,000 after a service life of 12 years. a) What amount had accumulated in a straight-line depreciation reserve at the end of the 5th year? b) Using double declining balance depreciation, determine the book value at the end of the 9th year. c) If the equipment was sold in the 6th year for $10,000, what sunk cost would...
A central air conditioning unit was installed on January 1, 2000at an initial cost of...
A central air conditioning unit was installed on January 1, 2000 at an initial cost of P650,000 and was expected to have a salvage value of P50,000 after a life of 7 years. a. What amount of depreciation had accumulated in a sum-of-the-years’-digit method at the end of 2003? b. Using the declining balance method, determine the depreciation charged for 2004 and the book value at the end of 2004. c. If the equipment was sold on Jan 1, 2005...
A firm is considering replacing the existing industrial air conditioning unit. They will pick one of...
A firm is considering replacing the existing industrial air conditioning unit. They will pick one of two units. The first, the AC360, costs $26,454.00 to install, $5,152.00 to operate per year for 7 years at which time it will be sold for $7,182.00. The second, RayCool 8, costs $41,990.00 to install, $2,150.00 to operate per year for 5 years at which time it will be sold for $9,054.00. The firm’s cost of capital is 6.22%. What is the equivalent annual...
A firm is considering replacing the existing industrial air conditioning unit. They will pick one of...
A firm is considering replacing the existing industrial air conditioning unit. They will pick one of two units. The first, the AC360, costs $26,708.00 to install, $5,045.00 to operate per year for 7 years at which time it will be sold for $7,180.00. The second, RayCool 8, costs $41,711.00 to install, $2,042.00 to operate per year for 5 years at which time it will be sold for $9,069.00. The firm’s cost of capital is 5.34%. What is the equivalent annual...
A firm is considering replacing the existing industrial air conditioning unit. They will pick one of...
A firm is considering replacing the existing industrial air conditioning unit. They will pick one of two units. The first, the AC360, costs $26,774.00 to install, $5,198.00 to operate per year for 7 years at which time it will be sold for $6,919.00. The second, RayCool 8, costs $41,604.00 to install, $2,063.00 to operate per year for 5 years at which time it will be sold for $9,086.00. The firm’s cost of capital is 5.80%. What is the equivalent annual...
A firm is considering replacing the existing industrial air conditioning unit. They will pick one of...
A firm is considering replacing the existing industrial air conditioning unit. They will pick one of two units. The first, the AC360, costs $26,197.00 to install, $5,052.00 to operate per year for 7 years at which time it will be sold for $7,031.00. The second, RayCool 8, costs $41,616.00 to install, $2,035.00 to operate per year for 5 years at which time it will be sold for $8,941.00. The firm’s cost of capital is 6.43%. What is the equivalent annual...
A firm is considering replacing the existing industrial air conditioning unit. They will pick one of...
A firm is considering replacing the existing industrial air conditioning unit. They will pick one of two units. The first, the AC360, costs $26,468.00 to install, $5,014.00 to operate per year for 7 years at which time it will be sold for $7,062.00. The second, RayCool 8, costs $41,121.00 to install, $2,143.00 to operate per year for 5 years at which time it will be sold for $9,074.00. The firm’s cost of capital is 5.40%. What is the equivalent annual...
1. A) A firm is considering replacing the existing industrial air conditioning unit. They will pick...
1. A) A firm is considering replacing the existing industrial air conditioning unit. They will pick one of two units. The first, the AC360, costs $26,294.00 to install, $5,151.00 to operate per year for 7 years at which time it will be sold for $6,930.00. The second, RayCool 8, costs $41,464.00 to install, $2,183.00 to operate per year for 5 years at which time it will be sold for $8,907.00. The firm’s cost of capital is 5.33%. What is the...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT