Question

In: Electrical Engineering

Define a 3 phase short circuit and a line to ground faults in a PV system....

Define a 3 phase short circuit and a line to ground faults in a PV system. How it affect the load and how it can be eliminated. Also make analysis on how it affect active and reactive power and the efficiency of the system.

Solutions

Expert Solution

These are very harsh faults and arise uncommonly in the power systems. These are also called as balanced faults and are of two types namely line to line to line (L-L-L) and line to line to line to ground (L-L-L-G)

The objectionable situation of current flowing through the grounding conductor is called as a line to ground fault in PV system. The reason for this unwanted current flow is an unintentional electrical connection between a current-carrying conductor in the PV system and the equipment grounding conductor (EGC).

The particular purpose of a ground-fault protection device (GFPD) as an element of a PV power system is used to reduce the hazard of fire-related with a ground fault. "If the ground fault is a short-circuit," the NJATC’s Photovoltaic Systems notes, "the fault current can be very high. In addition to being a protection risk, this generates a significant fire vulnerability as exposed metal is heated by the current flow."


Related Solutions

A 3 phase 450V (line-to-line), 1150rpm induction machine has the following equivalent circuit parameters. R1=0.33 Ohms,...
A 3 phase 450V (line-to-line), 1150rpm induction machine has the following equivalent circuit parameters. R1=0.33 Ohms, X1=1.3Ohms R2 = 0.25 Ohms X2 = 40Ohms. Determine the following: a) Rated stator current (per-phase) b) Input power factor c) Total power across the air gap d) The full-load torque e) Magnitude of the starting current
Define appropriate fault detection and protection system in a PV system (mini grid)
Define appropriate fault detection and protection system in a PV system (mini grid)
Q2.Find the equivalent circuit from no - load and short - circuit test of a 3...
Q2.Find the equivalent circuit from no - load and short - circuit test of a 3 - phase. 14.92 kW, 400 V, 6 - pole induction motor from the following test results (line values): No - load: 400 - V, 11 A, p.f. = 0.2 Short - circuit: 100 - V, 25 A, p.f. = 0.4 Rotor Cu loss at standstill is half the total Cu loss.
A 3-phase line has a resistance of 9 Ω/phase and a reactance of 23 Ω/phase. The...
A 3-phase line has a resistance of 9 Ω/phase and a reactance of 23 Ω/phase. The load at the receiving end is 130 MW at 0.8 p. f. lagging. Find the capacity of the synchronous condenser required to be connected at the receiving end to maintain the voltage at both ends of the transmission line at 132 KV.
A 3 phase 50Hz overhead line has the following constants: R/phase=2ohms; Xl/phase=10ohms and Y/phase=4x10^-4 siemens. The...
A 3 phase 50Hz overhead line has the following constants: R/phase=2ohms; Xl/phase=10ohms and Y/phase=4x10^-4 siemens. The line is supplying a balanced load of 24000 KVA, 0.8 pf lagging at 66KV. Compute for the sending end voltage, sending end current and efficiency of the line using: a.Nominal T Method b.Nominal pi Method c.Rigorous Method
Q2 (a) Define the meaning of the balanced supply in the three phase system. (2 marks)...
Q2 (a) Define the meaning of the balanced supply in the three phase system. (b) Distinguish four (4) possible configuration of the balanced three phase system. (c) The line voltages applied across the life terminals of a balanced four-wire system, star connected load are 400 V. The load impedance consists of a 4 Ω resistor that is in series with an inductor while the power factor of the system is equal to 0.75, assume the phase sequence is RYB. (i)...
A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of...
A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of 240 / 120 V. The primary and secondary resistances are 0.25 Ω and 0.05 Ω respectively, the corresponding leakage reactance being 0.75 Ω and 0.18 Ω. The transformer delivers current to the load at a 0.9 power factor lagging. Determine the voltage across the load.                                                                   Determine the power dissipated by the load.                                                          Determine percentage voltage regulation referred to the secondary...
B) 3 - phase system, consist of three lines is suspended by a string of 3...
B) 3 - phase system, consist of three lines is suspended by a string of 3 similar insulators. When the voltage across the line unit is 30 kV, calculate • The line to neutral voltage, when the shunt capacitance between each insulator and earth is 0.111 of the capacitance of the insulator itself. The string efficiency for the three insulators When you have 4 insulators How can you derive (V).
Define cost analysis on a off grid PV system (mini grid). Use necessary equations required on...
Define cost analysis on a off grid PV system (mini grid). Use necessary equations required on the summary. Write up of 10pages.
Q1 (a) (i) Mention the types of short circuit fault in power system network. (ii) Briefly...
Q1 (a) (i) Mention the types of short circuit fault in power system network. (ii) Briefly explain the effects of short-circuit type of faults on a power system network.