In: Electrical Engineering
1. Answer :- both loads
the rating of any one cord and plug connected utilization equipment not fastened in place shall not exceed 80 percent of the branch circuit ampere rating. The total rating of utilization equipment fastened in place , other than luminaries, shall not exceed 50 percent of the branch circuit ampere rating where lighting units, cord and plug connected utilization equipment not fastened in place, or both, are also supplied.
2. Answer :- false
the NMS cable shall not be permitted to battery storage rooms. Because, the non metallic sheath cable can be change its property. And there will be a chance to get a fault. So the NMS cable shall not be permitted to the battery storage rooms
3. Answer :- true
The safely carrying the maximum ground fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source. So, the earth shall not be considered as an effective ground fault current path.
4. Answer :- true
time switches shall be of the enclosed type or mounted on the suitable enclosures, a barrier shall be used around energized parts to prevent operator exposure when making manual adjustments or switching.
5. Answer :- true
the center grip of the operating handle of any switch or circuit breaker when in the highest position shall not be more than 6 feet 7 inches.
6. Answer :- false
the heating cable shall not be used with metallic lath ceilings.
7. Answer :- false
here, if the rating is more than 300 watts, we should use screw shell lamp holders.
8. Answer :- false
the 20 amp branch circuit supplying AC is permitte to supply lighting outlets.