Question

In: Mechanical Engineering

The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling...

The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling coil at a rate of 45m3 /min. The air cooling to the saturated state and leaving at a temperature of 16 °C. Determine: (10 points) a- Specific humidity at each state. b- Wet bulb and dew point temperatures at the final state c- Final relative humidity. d- Mass of water condensed. e- Rate of

heat removed from the air in kW. f- Show the process on Psychrometric chart.

Solutions

Expert Solution


Related Solutions

The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling...
The atmospheric air 32 °C dry bulb temperature and 70% relative humidity supplied to the cooling coil at a rate of 45m3 /min. The air cooling to the saturated state and leaving at a temperature of 16 °C. Determine: () a- Specific humidity at each state. b- Wet bulb and dew point temperatures at the final state c- Final relative humidity. d- Mass of water condensed. e- Rate of heat removed from the air in kW. f- Show the process...
300% excess air having a dry bulb temperature of 25 degree celsius and relative humidity of...
300% excess air having a dry bulb temperature of 25 degree celsius and relative humidity of 60% is used to fully combust 1 kg/hr of methane in a boiler and the heat of reaction is used to generate steam. Hot water enters the boiler as a saturated liquid at 102 degree celsius and leaves as superheated at 40 bar and 400 degree celsius. The combusted gases leave the boiler at 450 degree celsius and are then cooled to 25 degree...
Moist air at 55 oF dry bulb temperature and 40% relative humidity is first heated through...
Moist air at 55 oF dry bulb temperature and 40% relative humidity is first heated through a heating coil. The air is then adiabatically humidified by saturated water vapor at 4.5 psia. The exit air has a dry bulb temperature of 90 oF and wet bulb temperature 65 oF. Air is supplied at a volume flow rate of 478.5 cfm. Assume sea level pressure throughout. Determine the following. a) Show the inlet and outlet air condition clearly on the psychrometric...
USE EXCEL OR MATLAB IF YOU NEED Given the dry-bulb temperature, Tdb and relative humidity, Φ,...
USE EXCEL OR MATLAB IF YOU NEED Given the dry-bulb temperature, Tdb and relative humidity, Φ, the wet-bulb, Twb temperature may be calculated from the psychrometric equation (Jones, 1994): PvsΦ – Pss = PatmA (Twb -Tdb )                                              (1) Use your input from the Table below. The input Twb and Tdb are in oC (used in Eqs. (2) and (3) in Kelvin).    Pss = saturated vapor pressure at Twb (kPa) Pvs = saturated vapor pressure at Tdb (kPa)    Pss =...
Steam at 100°C is blown into an airstream at 21°C dry bulb, 50% saturation (Relative humidity),...
Steam at 100°C is blown into an airstream at 21°C dry bulb, 50% saturation (Relative humidity), at the rate of 1 kg steam/150 kg dry air. What is the final condition and show the process on the psychrometric chart? (Ans. Final moisture content (W2 = 0.0148 kgv/kg ; Final dry bulb temperature Tdb2=22.02°C ).
The dry- and wet-bulb temperatures of atmospheric air at 98 kPa are 28 and 14°C, respectively....
The dry- and wet-bulb temperatures of atmospheric air at 98 kPa are 28 and 14°C, respectively. Determine the following values.   1. The specific humidity in  kg H2O/kg dry air 2. The relative humidity in % 3. The enthalpy of air in  kJ/kg dry air
Air with a dry bulb temperature 75 F and a wet bulb temperature 65 F is...
Air with a dry bulb temperature 75 F and a wet bulb temperature 65 F is at a sea level pressure of 14.7 psia. Using equations to calculate (a) humidity ratio, (b) the relative humidity of the air, (c) enthalpy, (d) dew point, and (e) the mass density of the dry air. (50)
In an industrial process, it is required to maintain 30°C dry bulb temperature with high relative...
In an industrial process, it is required to maintain 30°C dry bulb temperature with high relative humidity equals to 60%. Determine the following air properties when the barometric pressure is standard, a) Dew point temperature; b) Specific humidity; c) Enthalpy of mixture per kg of dry air. d) Vapour density; e) Degree of saturation; f) Wet bulb temperature.
The air in a room has a pressure of 1 atm, a dry-bulb temperature of 24°C,...
The air in a room has a pressure of 1 atm, a dry-bulb temperature of 24°C, and a wetbulb temperature of 17°C. Using the psychrometric chart, determine (a) The specific humidity, (b) The enthalpy, in kJ/kg dry air, (c) The relative humidity, (d) The dew-point temperature, and (e) The specific volume of the air, in m3/kg dry air.
Air entering a dryer has a temperature (dry bulb) of 60°C and a dew point of...
Air entering a dryer has a temperature (dry bulb) of 60°C and a dew point of 26.7°C. Using the humidity chart, determine the actual humidity H, percentage humidity HP, humid heat cS and humid volume vH.