In: Electrical Engineering
External Faults in Power Transformer ::
External Short Circuit of Power Transformer
The short – circuit may occur in two or three phases of electrical power system. The level of fault current is always high enough. It depends upon the voltage which has been short-circuited and upon the impedance of the circuit up to the fault point. The copper loss of the fault feeding transformer is abruptly increased. This increasing copper loss causes internal heating in the transformer. Large fault current also produces severe mechanical stresses in the transformer. The maximum mechanical stresses occur during first cycle of symmetrical fault current.
High Voltage Disturbance in Power Transformer
High voltage disturbance in power transformer are of two kinds,
Transient Surge Voltage
High voltage and high frequency surge may arise in the power system due to any of the following causes,
Whatever may be the causes of surge voltage, it is after all a traveling wave having high and steep wave form and also having high frequency. This wave travels in the electrical power system network, upon reaching in the power transformer, it causes breakdown of the insulation between turns adjacent to line terminal, which may create short circuit between turns.
Power Frequency Over Voltage
There may be always a chance of system over voltage due to
sudden disconnection of large load. Although the amplitude of this
voltage is higher than its normal level but frequency is same as it
was in normal condition. Over voltage in the system causes an
increase in stress on the insulation of transformer. As we know
that, voltage,
increased voltage causes proportionate increase in the working
flux.
This therefore causes, increased in iron loss and proportionately
large increase in magnetizing current. The increase flux is
diverted from the transformer core to other steel structural parts
of the transformer. Core bolts which normally carry little flux,
may be subjected to a large component of flux diverted from
saturated region of the core alongside. Under such condition, the
bolt may be rapidly heated up and destroys their own insulation as
well as winding insulation.
Under Frequency Effect in Power Transformer
As, voltageas
the number of turns in the winding is fixed.
Therefore,
From, this equation it is clear that if frequency reduces in a
system, the flux in the core increases, the effect are more or less
similar to that of the over voltage.
Internal Faults in Power Transformer
The principle faults which occurs inside a power transformer are categorized as,
Internal Earth Faults in Power Transformer
Internal Earth Faults in a Star Connected Winding with Neutral Point Earthed through an Impedance
In this case the fault current is dependent on the value of earthing impedance and is also proportional to the distance of the fault point from neutral point as the voltage at the point depends upon, the number of winding turns come across neutral and fault point. If the distance between fault point and neutral point is more, the number of turns under this distance is also more, hence voltage across the neutral point and fault point is high which causes higher fault current. So, in few words it can be said that, the value of fault current depends on the value of earthing impedance as well as the distance between the faulty point and neutral point. The fault current also depends up on leakage reactance of the portion of the winding across the fault point and neutral. But compared to the earthing impedance,it is very low and it is obviously ignored as it comes in series with comparatively much higher earthing impedance.
Internal Earth Faults in a Star Connected Winding with Neutral Point Solidly Earthed
In this case, earthing impedance is ideally zero. The fault current is dependent up on leakage reactance of the portion of winding comes across faulty point and neutral point of transformer. The fault current is also dependent on the distance between neutral point and fault point in the transformer. As said in previous case the voltage across these two points depends upon the number of winding turn comes across faulty point and neutral point. So in star connected winding with neutral point solidly earthed, the fault current depends upon two main factors, first the leakage reactance of the winding comes across faulty point and neutral point and secondly the distance between faulty point and neutral point. But the leakage reactance of the winding varies in complex manner with position of the fault in the winding. It is seen that the reactance decreases very rapidly for fault point approaching the neutral and hence the fault current is highest for the fault near the neutral end. So at this point, the voltage available for fault current is low and at the same time the reactance opposes the fault current is also low, hence the value of fault current is high enough. Again at fault point away from the neutral point, the voltage available for fault current is high but at the same time reactance offered by the winding portion between fault point and neutral point is high. It can be noticed that the fault current stays a very high level throughout the winding. In other word, the fault current maintain a very high magnitude irrelevant to the position of the fault on winding.
Internal Phase to Phase Faults in Power Transformer
Phase to phase fault in the transformer are rare. If such a fault does occur, it will give rise to substantial current to operate instantaneous over current relay on the primary side as well as the differential relay.
Inter Turns Fault in Power Transformer
Power transformer connected with electrical extra high voltage transmission system, is very likely to be subjected to high magnitude, steep fronted and high frequency impulse voltage due to lightening surge on the transmission line. The voltage stresses between winding turns become so large, it can not sustain the stress and causing insulation failure between inter – turns in some points. Also LV winding is stressed because of the transferred surge voltage. Very large number of power transformer failure arises from fault between turns. Inter turn fault may also be occurred due to mechanical forces between turns originated by external short circuit.
Core Fault in Power Transformer
In any portion of the core lamination is damaged, or lamination of the core is bridged by any conducting material that causes sufficient eddy current to flow, hence, this part of the core becomes over heated. Sometimes, insulation of bolts (Used for tightening the core lamination together) fails which also permits sufficient eddy current to flow through the bolt and causing over heating. This insulation failure in lamination and core bolts causes severe local heating. Although these local heating, causes additional core loss but can not create any noticeable change in input and output current in the transformer, hence these faults cannot be detected by normal electrical protection scheme. This is desirable to detect the local over heating condition of the transformer core before any major fault occurs. Excessive over heating leads to breakdown of transformer insulating oil with evolution of gases. These gases are accumulated in Buchholz relay and actuating Buchholz Alarm.
3. Early discovery of the failures
It is unnecessary to say that the sooner a failure is detected, the better for the transformer, and it requires a careful and detailed maintenance and inspection. There are procedures made for the regular inspection and of routine.
By means of this inspection a failure can be detected before it becomes serious, and reduce any damage in whatever possible.
Some defects are caused by reasons beyond human control, such as sudden transformer failures and defects that develop slowly. Let’s describe each of these non-human related reasons.
Sudden transformer failures
Most of the dielectric interruptions occur suddenly, especially due to lightning or to an abnormal tension, causing a direct failure. Excessive current by an external short circuit or by a mechanical hit also happen suddenly.
Disturbances by earthquakes and fires can accidentally damage the transformer.
Defects that develop slowly
Sudden defects are related generally to totally external or foreign factors to the transformer of such form that it is outside of our scope the power to foresee them and to prepare us to face these.
The objective of transformer maintenance and inspection is to discover the defects that occur and that may develop slowly. These defects are described below //
3.2.2 Deformation of the insulation materials and of the transformer windings, due to mechanical blows caused by an external short circuit. The transformer generally is designed and is manufactured to resist the heat and the mechanical blows. However, if it is exposed to frequent and intensive mechanical blows, even a small deformation can be converted into a serious internal defect.
Insulation of the core. There can be poor insulation between the sheets of the core, between the tightening screw of the core and the insulation pipe, etc. The poor insulation cause a short circuit in the magnetic flow, producing a constant short circuit current flow in this place and generating excessive heating up which can lead to serious defects.
Poor insulation due to a harsh operational condition such as excessive load. According to what was mentioned in the instruction manual, the insulation of the transformer deteriorates by the increase in the temperature and this deterioration over the years worsens and is converted into a serious failure when the transformer suffers an excessive load.
Deterioration of the insulation materials such as oil, bushings, etc. due to moisture absorption, to oxidation and to formation of a partial discharge, etc.
Deterioration of the external insulation of the transformer due to wind, snow, salt and dust. This can be prevented with the correct inspection and maintenance.
3.2.7 Defects in the accessories, oil leak, gas leak, etc.
Leaking oil from corroded transformer (photo credit: kijinc.com)
Go back to Transformer Failure Topics
Internal defects of the transformer
Defects in the winding
Short circuits – There are short circuits between the turns, between the phases and between the windings. Most short circuits failures are caused by abnormal tensions on the surge arresters and others because of the deterioration of the insulation oil and to the penetration of rain.
Also, some short circuits are caused by the deterioration because of heat, caused by an electromagnetic mechanical force or by an abnormal excessive load.
Generally, as secondary effect, internal short circuits cause serious deformations to the windings.
Breakage of the terminals of the winding – The terminals of the spooled suffer damages by an excess of current (external short circuit, etc) or by a lighting strike. Also, the short circuit accidents of the system that accumulate, cause damages on the supports of the windings, by their repetitive mechanical destructive force, that finally break the terminals.
Short circuit to ground – The impulse voltage or the deterioration of the insulation can cause a short circuit to the grounding of the winding or of its terminal to the core or to the tank. The mentioned defects can be detected easily through an external diagnosis or an electrical monitoring.
Defects in the core
There are defects due to poor insulation of the tightening screws of the core, or an oil-cooling duct obstructed, that cause excessive heating of the core. The defects on the core develop slowly.
The insulation and the poor grounding contact already mentioned, cause a partial short circuit current, a deterioration of the oil of the insulation materials in their surroundings, which gradually are converted into serious failures.
A poor or loose tightening between the core and the clamps of the windings can cause damaging vibrations.
Go back to Transformer Failure Topics ↑
5. How to detect internal failures?
As additional protection, use the different relays that the transformer has to detect and be protected of failures. Next you can find which parts are used to protect the transformer from internal failures: