Question

In: Other

In a device to produce drinking water, humid air at 32C, 90% relative humidity and 1...

In a device to produce drinking water, humid air at 32C, 90% relative humidity and 1 atm is cooled to 5C at constant pressure. If the duty on the unit is 2,200 kW of heat is removed from the humid air.

Data: Air at 32C has H = 0.204 kJ/mol and at 50C has H = -0.576 kJ/mol

H of steam can be found on the steam tables – vapor at 32C and 1 atm; vapor at 5C and liquid at 5C. Assume the volume of the humid air follows the ideal gas law.

H of water liquid at 5C = 21 kJ/kg; vapor at 5C = 2510.8 kJ/kg; H of water vapor at 32C = 2560.0 kJ/kg

What is the flow of humid air entering the system in mol/min?

What is the flow of humid air entering the system in m^3?

How much drinking water is produced by the system in lit/min?

Solutions

Expert Solution

1) Relative humidity = partial pressure of water/vapor pressure of water*100

vapor pressure of water at 32 DegC = 4.75925 kPa, and 1 atm = 101.325 kPa, partial pressure = totla pressure*mole fraction of water

0.9 = 101.325*mole fraction of water/4.75925

so mole fraction of water in entering humid air = 0.04227

now assuming water vapor in equilibirium finally,

mole fraction of water in outgoing humid air = water vapor pressure at 5 DegC/total pressure

=0.872575/101.325 = 0.0086116

Now lets assume n moles of humid air are entering to system

water mass enetering = mole*molar mass = n*0.04227*18/1000 Kg

mole of dry air entering = n(1-0.04227) = 0.95773n moles

moles of dry air in outlet vapor stream = same = 0.95773n(since dry air will not condense)

lets assume moles of water in outlet humid air = y

then mole of water = y/(y+0.95773n) = 0.0086116 so y = 0.0083192n moles

or mass of water vapor in outlet air = n*0.0083192*18/1000 Kg

so water mass condensed = inlet mass - outlet vapor mass =

n*0.04227*18/1000 Kg - n*0.0083192*18/1000 Kg = 0.0339508n*18/1000 Kg

applying enthalpy balance:

(Enthalpy in) - (enthalpy going out) = enthalpy change

[0.95773n*0.204 +n*0.04227*18/1000*2560] - [0.95773n*(-0.576)+n*0.0083192*18/1000*2510.8 + 0.0339508n*18/1000*21] = 2200

solving for n we get, n = 954 mol/s

mol/min of humid air entering = 954*60 = 57241.57

2) applying PV = nRT for humid air

101325*V = 57241.57*8.314*(273+32) or V = 1432.53 m3/min

3) As calculated in part 1, water condensed = 0.0339508n*18/1000 = 0.0339508*57241.57*18/1000

= 34.98 Kg/min

density of water = 1 kg/liter,

so liter /min = 34.98 lit/min


Related Solutions

Humid air at 300 kPa, 10°C, and 90% relative humidity is heated in a pipe at...
Humid air at 300 kPa, 10°C, and 90% relative humidity is heated in a pipe at constant pressure to 50°C. Calculate the amount of heat, in kJ/kg dry air, required
Humid air at 155 kPa, 40°C, and 70 percent relative humidity is cooled at constant pressure...
Humid air at 155 kPa, 40°C, and 70 percent relative humidity is cooled at constant pressure in a pipe to its dew-point temperature. Calculate the heat transfer, in kJ/kg dry air, required for this process. Use data from the tables. The heat transfer is  kJ/kg dry air.
If at 30F the air has 25% relative humidity, what is the relative humidity at 70F...
If at 30F the air has 25% relative humidity, what is the relative humidity at 70F and how much moisture must be added to get it up to 50% relative humidity.
Air enters a window air conditioner at 1 atm, 36oC and 75% relative humidity (??) at...
Air enters a window air conditioner at 1 atm, 36oC and 75% relative humidity (??) at a rate of 12m3/min and it leaves as saturated air at 18oC. Part of the moisture in the air which condenses during the process is also removed at 18oC. Determine (a) the rate of heat (Q?) and (b) moisture removal from the air. (c) What-if Scenario: What would the rate of heat removal be if moist air entered the dehumidifier at 95 kPa instead...
Relative humidity isn't everything. Why is it that outdoor air of 80 Fo at 55% humidity...
Relative humidity isn't everything. Why is it that outdoor air of 80 Fo at 55% humidity will feel more “muggy” than a 50 Fo cave at 75% humidity? What other parameter is a better measure of the actual amount of moisture in the air, and how do we define it? Then give two examples of when keeping close track of moisture in the air is important.
Relative humidity isn't everything. Why is it that outdoor air of 80 Fo at 55% humidity...
Relative humidity isn't everything. Why is it that outdoor air of 80 Fo at 55% humidity will feel more “muggy” than a 50 Fo cave at 75% humidity? What other parameter is a better measure of the actual amount of moisture in the air, and how do we define it? Then give two examples of when keeping close track of moisture in the air is important.
Outside air at 10 degC, 1 bar and 40% relative humidity enters an air conditioner operating...
Outside air at 10 degC, 1 bar and 40% relative humidity enters an air conditioner operating at steady state with a mass flow rate of 1.5kg/s. The air is first heated at essentially constant pressure to 30 degC. Liquid water at 15 degC is then injected, bringing the air to 25 degC, 1bar. Determine (a) the rate of heat transfer to the air passing through the heating section, in kJ/s. (b) the rate of water is injected, in kg/s. (c)...
At 200 C relative humidity of 1 m3 of air is 60%. when temperature is kept...
At 200 C relative humidity of 1 m3 of air is 60%. when temperature is kept constant and volume is reduced to 0.25 m3 find the mass of moist air that would be condensed. SVP of water at 200 C = 17.5mmHG R= 8.31 J mol-1 K-1
Air enters an air conditioning unit at 32oC, 80% relative humidity, and with a mass flowrate...
Air enters an air conditioning unit at 32oC, 80% relative humidity, and with a mass flowrate of 12 kg/min. It is to be conditioned to 25oC and 50% relative humidity. In order to do this, part of the moisture in the air must be removed as condensate at 30oC. Be able to draw the path that the atmospheric air takes on the psychrometric chart. Find a. The rate of moisture removal from the air, mw  b. The rate of...
An air conditioning system is to take outdoor air at 30 oC and 70% relative humidity...
An air conditioning system is to take outdoor air at 30 oC and 70% relative humidity at a steady rate of 10 m3/s and to condition it to 25 oC and 50% relative humidity. The outdoor air is first cooled down to 13.9 oC using cooling coil and then heated to the desired condition in the heating section. Assuming the air is at 1 atm pressure, Draw the air conditioning process on the attached psychometric chart. Determine the mass flow...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT