A power line 50km long has a total resistance of 0.60ohm. A generator produces 100V at 70A. in order to reduce energy loss due to heating of the transmission line, the voltage is stepped up with a transformer with a primary to secondary turns ratio of 1 to 100. What percentage of the original energy is lost when the transformer is not used?
Thermal power
consumed by the transmission line due to its
resistance:
P(c)=RI^2
Where P(c) is power consumed
I= produced power divided by produced
voltage:
I=P/V
(1) In the case before voltage was raised
I=P/V=7000/100=70 A
Thermal power consumed in this case:
P(c)=RI^2=0.6*(70)^2=2940 Watt
Lost power percentage=2940/7000= 42.0%
(2) In the case after voltage has been raised:
P=IV(produced power)
When P is constant then we have
IV=constant ? I1V1=I2V2 ? I2/I1=V1/V2
I2/I1=100/100K=1/1000
And since the lost power percentage is directly proportional to
(I^2)
then the ratio between the lost power after and before the voltage
raising is equal to (I2/I1)^2 =(1/1000)^2=1/10^6
In math language: P(c)2/P(c)1=(I2/I1)^2=1/10^6
This implies that: P(c)2=P(c)1/10^6
then lost power percentage after voltage raising = 42/10^6 =
42*10^-6%
The second part can be obtained the same way the first part was
done as follows:
I=P/V=7000/100000=0.07A
P(c)=RI^2=0.6*(0.07)^2= 0.00294 watt
Lost power percentage in this
case=0.00294/7000=42*10^-6%