77 kW is to arrive at a town over two 0.140 ? lines. Estimate how much power is saved if the voltage is stepped up from 240 V to 2400 V and then down again, rather than simply transmitting at 240 V . Assume the transformers are each 99% efficient.
Without the transformers, we can find the delivered current,
which is the current in the transmission lines, from the delivered
power:
Pout=
IVout
77*10^3 W = I*(240V), which gives I = 320.833A.
The power loss in the lines is
PL0= I^2*Rlines= ((320.833)^2)*2*(0.140) = 28821.46 = 28.821 kW
With the transformers, to deliver the same power at 240V, the delivered current from the step-down transformer is still 320.833A.
If the step-down transformer is 99% efficient, we have
(0.99)Ip2Vp2 = Is2Vs2;
(0.99)Ip2(2400V) = (320.833 A)(240V), which gives Ip2 = 32.40 A.
Because this is the current in the lines, the power loss in the lines is
PL2 = Ip22Rlines = (32.40 A)^2*(2)(0.140W) = 293.93 W = 0.293 kW
For the 1% losses in the transformers, we approximate the power in each transformer.
PLt = (0.01)(77 kW + 77.14 kW) = 1.54kW.
The total power loss using the transformers is
PL = 0.293kW + 1.54kW = 1.833 kW.
The power saved by using the transformers is
Psaved = PL0 - PL = 28.821 kW - 1.833kW = 26.988 kW.