A manufacturing operation requires 50 fc on the workplane in a 100 ft x 150 ft facility. The walls and ceilings are painted white. The work plane is 25 feet below the lights.
1. Calculate how many high-bay 400-W metal halide fixtures are required
2. Calculate how many 6-lamp T8 HBF fixtures are required.
Given data,
Both walls and ceilings are white ,
Rc = reflectivity of ceiling = 100%
Rw = reflectivity of walls = 100%
Ew = 50 fc ,
H = height = 25 ft,
W = width = 150 ft ,
L = length = 100 ft ,
Area of work plane (A) = W*L = 15000 ft2 ,
Room-Cavity Ratio (RCR)
RCR = 5H*(W + L) / (W*L)
= 5*25*(150 + 100) / (150*100)
= 2.08 ~ 2
1. Number of high-bay 400-W metal halide (N)
From CU table,
Coefficient of Utilization (CU) for 400-W metal halide =
0.80
Lumens Per Fixture (LPF) for 400-W metal halide = 23,500 lm
Now,
N = (Ew * A) / (CU * LPF)
= (50 * (100 * 150)) / (.80 x 23,500)
= 39.89 ~ 40 lights
2. Number of 6-lamp T8 HBF (N)
Coefficient of Utilization (CU) for 6-lamp T8 HBF = 0.82
Lumens Per Fixture (LPF) for 6-lamp T8 HBF = 20,500 lm
N = (Ew * A) / (CU * LPF)
= (50 * (100 * 150)) / (.82 x 23,500)
= 44.61 ~ 45 lights