The kVA laod as given would be:
kW/power factor = 6.1 MW / 0.93 = 6.56 MVA
Total current then would be 6,559,140 VA / (18,000*1.731) = 210.4
amps. This assumes a three phase source since at 6.56 MVA it is not
likely it would be single phase.
If it was the total current would be 6.56 MVA / 0.018MV = 364.4
Amps as you have stated.
I will stick with single phase because you assumed it or know it to
be the case.
So we know the we have 6.56 MVA @ arccos(0.93) degrees = 6.56 MAV @
21.57 degrees.
Convert this number to Rectangular notation:
6.56 MVA @ 21.57 degrees = 6.56 MVA*Cosine (21.57) +j 6.56 MVA*Sine
(21.57) =
6.10 MW + j 2.41 MVAR, I assummed a lagging power factor since you
stated you will be correcting it with capacitors. So to correct to
a power factor of 1.0 you must add exactly the same number of MVARS
of capacitance or -j 2.41 MVAR
To get: 6.10MW+j2.41 MVAR -j2.41 MVAR = 6.10 MW +j0 = 6.10 VA 2 0
degrees = 6.10 MW.
The station will be delivering exactly the same amount of "POWER"
but you should notice that teh MVA value decreased from 6.56 MVA @
21.57 degrees to 6.10 MVA @ 0.0 degrees. The affect of correcting
the power factor does notchange the power delivered but does change
the MVA by reducing teh power factor angle to zero.