PROBLEM: Ammonia is used as a refrigerant. It is compressed outdoors, and the ammonia is then...

PROBLEM: Ammonia is used as a refrigerant. It is compressed outdoors, and the ammonia is then liquefied and circulated through the refrigerator's evaporator heat exchanger. The evaporator is indoors. The room containing the evaporator has a net open volume of 1000 m3 and a ventilation rate equal to two air changes per hour. A leak develops in an ammonia line that results in 50 g of ammonia being released per minute. 1. How long will it take for the ammonia concentration to increase to the PEL concentration? 2. How long will it take to reach the IDLH concentration? 3. If the flow of ammonia is stopped at the time the IDLH concentration is reached, how long will it be before the concentration is reduced to the PEL concentration? You may assume that the mixtures of gases are ideal at the low pressures involved. Also assume that the ammonia is mixed with the air in the room completely and instantaneously and that the air- ammonia mixture leaving the room has the same concentration as the mixture in the room. Hint: Use a differential equation and separation of variables to solve.

Solutions

Expert Solution

It's an interesting question. Let's start with noting down the 'Permissible Exposure Limit' (PEL) and 'Immediately Dangerous to Life or Health' (IDLH) for Ammonia#

OSHA PEL for Ammonia = 50 ppm (35 mg/m3)

IDLH for Ammonia = 500 ppm (350 mg/m3)

The problem says that due to the leak NH3 is leaking into the room (of volume 1000 m3) and the ventilation not being high enough, NH3 concentration is building inside the room. As a result, first it will reach the PEL limit and if the leak continues, the NH3 concentration will reach the IDLH limit.

To solve all the parts, we have to first develop the equation relating the NH3 concentration with time. To do this, write the material balance for NH3 in the control volume (the control volume here is the room itself).

FINNH3 - FOUTNH3 = Accumulation of NH3 inside the room..................(1)

............(2) (Here, I've converted the leak rate for NH3 (given in mass) to molar leak rate by dividing it with the molecular mass of NH3 (which is 17))

The ventilation rate has been given as 2 air changes per hour. This basically means that the ventilation system is able to replenish twice the volume of the room in an hour. This basically means the ventilation flow rate is (This is basically 2 multiplied by the volume of the room divided by the time in minutes)

If you need a formula, it would be something like this:

Flow rate in m3/h = Number of air changes * Volume of the room / time

The ventilation rate is therefore,

Therefore, .......(3)

Accumulation is given by the diferential form as follows:

.........(4)

Putting (2), (3) and (4) into (1) yields:

-------------(5)

(5) is a differential equation which can be solved by separation of variables as follows:

Integrating both sides and placing the limits to integration:(The initial concentration is 0 (at t=0) and at time =t is CNH3)

Separation of variables basically means to separate the two variables by taking each variable to different sides of the equation and integrating both sides.

For Part (a) we are required to find the time when the final concentration (CNH3) becomes (Converting weight to moles by dividing by molecular mass of NH3 and dividing by 1000 to convert mg to grams)

Putting CNH3 = 0.002059 mol/m^3 in equation (6):

For part (b) we are required to find the time when the final concentration (CNH3) becomes (Converting weight to moles by dividing by molecular mass of NH3 and dividing by 1000 to convert mg to grams)

Putting CNH3 = 0.02059 mol/m^3 in equation (6):

For Part (c), we need to rewrite the mass balance, as the leakage has been arrested, thereby making  

(FNH3OUT still remains unchanged)

Accumulation term is the same. The differential equation thus becomes:

Solving by separation of variables:

..........(7)(The limits indicate that we wnat to get to the PEL limit (i.e. 0.002059 mol/m^3) from the IDLH limit (i.e. 0.02059 mol/m^3))

't' is the time that it takes to reduce the concentration from 0.02059 mol/m^3 to 0.002059 mol/m^3

Therefore, it would take 69.0845 min to reduce the concentration from the IDLH level to PEL level

Hope this helps!


Related Solutions

A commercial refrigerant that uses R-134a as the refrigerant is used for cooling, to keep the...
A commercial refrigerant that uses R-134a as the refrigerant is used for cooling, to keep the condition at -35o, throws heat into the cooling water that has been in the condenser at 18oC and 0.25kg / s and has been formed since 26o. The refrigerant enters the condenser at 1.2 MPa and 50o ° and exits by cooling 5o C more than the saturation temperature at the same pressure. If the compressor consumes 3.3 kW (Answer: 0.0498 kg / s,...
Refrigerant 134a enters an air conditioner compressor at 4 bar, 20°C, and is compressed at steady...
Refrigerant 134a enters an air conditioner compressor at 4 bar, 20°C, and is compressed at steady state to 12 bar, 80°C. The volumetric flow rate of the refrigerant entering is 7.5 m3/min. The work input to the compressor is 112.5 kJ per kg of refrigerant flowing. Neglecting kinetic and potential energy effects, determine the magnitude of the heat transfer rate from the compressor, in kW.
Design a refrigerator working on propane ammonia and R407C refrigerant and producing -20K, -10K and O...
Design a refrigerator working on propane ammonia and R407C refrigerant and producing -20K, -10K and O K temperature during steady state operation.... carryout experimental validation using appropriate software. write energy and exergy equation in Fortran 77 only... plot graph in scilab....
The Great Outdoors is a company that manufactures canvas used for tents. The company needs to...
The Great Outdoors is a company that manufactures canvas used for tents. The company needs to purchase new pressing equipment. The vice president of finance is considering two mutually exclusive presses. Each requires an initial investment of $100,000. The president of the company has stated that he wants a maximum payback period of 4 years. The cash inflows associated with each press are shown in the following table: Cash Inflows Year Press A Press B 1 $10,000 $40,000 2 $20,000...
CCl F is considered to be environmentally safe and is used as a refrigerant. The heat...
CCl F is considered to be environmentally safe and is used as a refrigerant. The heat of vaporization of CCl F is 289 J/g. What mass of this substance must evaporate in order to freeze 2 moles of water initially at 20°C? The heat of fusion of water is 334 J/g and the specific heat of water is 4.18 J/g-K.
A commercial refrigerator with refrigerant 134a as the working fluid is used to keep the refrigerated...
A commercial refrigerator with refrigerant 134a as the working fluid is used to keep the refrigerated space at TL = -35°C by rejecting waste heat to cooling water that enters the condenser at 18°C at a rate of 0.25 kg/s and leaves at 26°C. The refrigerant enters the condenser at 1.2 MPa and 50°C and leaves at the same pressure and 41.3°C. If the compressor consumes 3.3 kW of power, determine (a) the mass flow rate of the refrigerant, (b)...
What is a compressed Air Turbine? What’s it used for ? Benefits? How is a mechanical...
What is a compressed Air Turbine? What’s it used for ? Benefits? How is a mechanical break used with it ?
The spring shown in the figure is compressed 52 cm and used to launch a 100...
The spring shown in the figure is compressed 52 cm and used to launch a 100 kg physics student. The track is frictionless until it starts up the incline. The student's coefficient of kinetic friction on the 30∘ incline is 0.19 . Part A What is the student's speed just after losing contact with the spring? Express your answer to two significant figures and include the appropriate units. Part B How far up the incline does the student go? Express...
A Bottle of compressed nitrogen is used in your laboratory to flush the CVD furnace. If...
A Bottle of compressed nitrogen is used in your laboratory to flush the CVD furnace. If you received the 20-liter bottle at room temperature (25°C) and 10 MPa. After the slow release of nitrogen (isothermal), estimate the pressure if you have disbursed 1 kg. * 2 points 4 MPa 5 MPa 5.6 MPa 4.4 MPa Other:
Refrigerant R134a is entering a condenser and is being cooled by water. The refrigerant enters the...
Refrigerant R134a is entering a condenser and is being cooled by water. The refrigerant enters the condenser with a mass flow rate of 6 kg/min at 1 MPa and 70 0C and leaves at 35 0C. The cooling water enters at 300 KPa and 15 0C and leaves at 25 0C. Neglecting any pressure drop, determine: The mass flow rate of the cooling water The heat transfer rate from the refrigerant to the water. The rate of entropy production within...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT