Question

In: Other

A pipe of outside diameter 200 mm is lagged with an insulating material of thermal conductivity...

A pipe of outside diameter 200 mm is lagged with an insulating material

of thermal conductivity 0.06 W m–1 K–1 and thickness 75 mm. The pipe

carries a process fluid at a temperature of 300 °C and the average

temperature of the outer surface of the lagging is 45 °C.

(a) Estimate the rate of heat loss per metre length of pipe.

(b) Explain why the thermal resistance of the pipe wall can be ignored.

4. A pipe carrying superheated steam at 300 °C has an outside diameter of

120 mm and is lagged with two layers of insulating material. The first

layer (adjacent to the outer pipe wall) is 25 mm thick and has a thermal

conductivity of 0.072 W m–1 K–1. The second layer (covering the first

layer) is 20 mm thick, has a thermal conductivity of 0.051 W m–1 K–1 and

an outside temperature of 28 °C.

Estimate the rate of heat loss per metre length of pipe (assume the thermal

resistance of the pipe wall is negligible).

Solutions

Expert Solution

a)

Rate of heat loss/ metre = 171.57 W/m

b) For calculating heat flow across an insulated pipe, Thermal resistance(RT) must be calculated for every layer of insulation.

Thermal resistance varies with the insulation thickness of each layer, their respective thermal conductivities, outer pipe diameter and the temperature of the pipe.

RT = ln (r2/r1)/2LK

Where,

r2 = outside diameter + thickness of insulation

r1 = outside diameter

L = length of the pipe

K = thermal conductivity of the pipe.

In rate of heat transfer calculation, RT takes into account all the parameters of the pipe.

Q=(To -T1)/RT

To - outside temperature

T1 -- inside temperature

4)

K1 -- thermal conductivity of the 1st layer of insulation.

K2 --- thermal conductivity of 2nd layer of insulation.

rate of heat loss/ metre = 190.43 W/m


Related Solutions

The thermal conductivity of an insulating material used over a hot pipe varies as k =...
The thermal conductivity of an insulating material used over a hot pipe varies as k = 0.0545 (1 + 28.4 × 10–4 T) where T is in °C and k is in W/mK. This insulation is used for a thickness of 12 cm over a pipe of diameter 0.6 m. The pipe surface is at 300°C and the outside insulation temperature is 60°C. Determine the heat flow for a length of 5 m. Also find the mid layer temperature.
A new material has a measured thermal conductivity k of 200 BTU-in/hr-ft2 -°F. Is this material...
A new material has a measured thermal conductivity k of 200 BTU-in/hr-ft2 -°F. Is this material a thermal insulator or a conductor? Calculate the R and U values for a block of this material that is 3 inches thick. Now sandwich this block of material between two sheets of R-0.8 fiberboard. What is the new effective U value?
Water is flowing through a pipe having the diameter 200 mm and 100 mm at sections...
Water is flowing through a pipe having the diameter 200 mm and 100 mm at sections 1 and 2 respectively. The rate of flow through the pipe is 35 liters per second. The section 1 is 6000 mm and section 2 is 4000 mm above the datum line. If the pressure at the section 1 is 0.4 N/mm2, find the intensity of pressure at section 2.                                                            
A rod of diameter D = 25 mm and thermal conductivity of 60 W/m·K protrudes from...
A rod of diameter D = 25 mm and thermal conductivity of 60 W/m·K protrudes from a furnace with a wall temperature of 200ºC. The rod is welded to the furnace wall and is used as a hangar for instrumentation cables. To avoid damaging the cables, the surface temperature of last 100 mm of the rod must be kept below 100ºC. The ambient air temperature is 25ºC and the convection coefficient is 15 W/m2K. (a) Write the finite-difference equation for...
A 30 m long pipe with an outside diameter of 75 mm is used to deliver...
A 30 m long pipe with an outside diameter of 75 mm is used to deliver steam at a rate of 2000 kg / hour. The vapor pressure is 198.53 kPa entering the pipe with a quality of 98%. The pipe needs to be given insulation with thermal conductivity of 0.2 W / (m K) so that the vapor quality only slightly decreases to 95%. The outer surface temperature of the insulation is assumed to be 25 ° C. Ignore...
A pipe, 900 m long and 200 mm in diameter discharges water to the atmosphere at...
A pipe, 900 m long and 200 mm in diameter discharges water to the atmosphere at a point 10 m below the inlet level. With an inlet pressure of 40 kPa gauge, the flow rate is 40 litres/sec. At a point half way between the pipe inlet and outlet, a new tapping is made from which water is taken at a rate of 18 litres/sec. To what value must the inlet pressure be raised in order to maintain the same...
A long, cylindrical, electrical heating element of diameter D= 10 mm, thermal conductivity k= 240 W/m·K,...
A long, cylindrical, electrical heating element of diameter D= 10 mm, thermal conductivity k= 240 W/m·K, density ρ= 2700 kg/m3, and specific heat cp= 900 J/kg·K is installed in a duct for which air moves in cross flow over the heater at a temperature and velocity of 27°C and 15 m/s, respectively. (a) Neglecting radiation, estimate the steady-state surface temperature when, per unit length of the heater, electrical energy is being dissipated at a rate of 1500 W/m. (b) If...
) A 50 mm-diameter propeller was installed in a 150 mm-diameter water pipe and the propeller...
) A 50 mm-diameter propeller was installed in a 150 mm-diameter water pipe and the propeller speed was measured for a range of water discharge in the pipe. The water had a density and dynamic viscosity of 1000 kg/m3 and 0.00112 Ns/m2 respectively. The measured results were as follows: Q (litres/s): 12 28 45 63 95 120 160 180 N (rps): 5 10 15 20 30 40 60 80 Plot the dependence of propeller coefficient against propeller Reynolds number. A...
(c) A 50 mm-diameter propeller was installed in a 150 mm-diameter water pipe and the propeller...
(c) A 50 mm-diameter propeller was installed in a 150 mm-diameter water pipe and the propeller speed was measured for a range of water discharge in the pipe. The water had a density and dynamic viscosity of 1000 kg/m3 and 0.00112 Ns/m2 respectively. The measured results were as follows: Q (litres/s): 12 28 45 63 95 120 160 180 N (rps): 5 10 15 20 30 40 60 80 Plot the dependence of propeller coefficient against propeller Reynolds number. A...
Water flows through a cast iron pipe with a diameter of 30 mm. The pipe is...
Water flows through a cast iron pipe with a diameter of 30 mm. The pipe is inclined at an angle of 3 degrees from horizontal and is 40 m long. The water flows due to gravity only. What is the maximum volume flow rate of the water? You may ignore any minor loses.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT