Question

In: Other

It is desired to cool down (0.37) kg/s of an aqueous solution with a heat capacity...

It is desired to cool down (0.37) kg/s of an aqueous solution with a heat capacity similar to water from 60 to 50oC. The cooling fluid will be (0.33) kg/s of water at 25oC. A double-pipe heat exchanger will be used. The external diameter of the interior tube is 0.025 m. The overall heat transfer coefficient is estimated as 1,600 W/(m2.K). Calculate the necessary tube length if:

  1. A countercurrent arrangement is used.
  2. A co-current arrangement is used.

Solutions

Expert Solution

Assuming the cooling water is used in interior tube.

We are given double pipe heat exchanger using water inside the pipe and aqueous solution between the annular space, used to cool aqueous solution at to and the inlet temperature of water is,

The mass flow rate of cold liquid, water is given as,

The mass flow rate of hot liquid, aqueous solution is given as,

Applying energy balance across the heat exchanger we get,

The heat capacity of the water and aqueous solution and can be taken as,

So the outlet temperature of the water will be 36.210C

and heat transferred is given as,

a. Now for counter current, (right of the image),

Logarithmic mean temperature difference for counter current heat exchanger is defined as,

Now the heat transferred in the heat exchanger between the hot fluid and cold fluid is given as,

Overall heat transfer coefficient is given as,

Area of the heat transfer is given as,

external diameter of the interior tube is given as,

So,

So the length of the pipe needed for counter current arrangement is 5.053 m

b. Now for co current, (left of the image),

Logarithmic mean temperature difference for co-current heat exchanger is defined as,

Now the heat transferred in the heat exchanger between the hot fluid and cold fluid is given as,

So the length of the pipe needed for co-current arrangement is 5.413 m


Related Solutions

Determination of heat capacity of calorimeter trial 1 trial 2 trial 3 volume of cool water...
Determination of heat capacity of calorimeter trial 1 trial 2 trial 3 volume of cool water 50.0 mL 50.0mL 50.0mL volume of warm water 50.0 mL 50.0 mL 50.0 mL initial temp of cool water=initial calorimeter temp 25.2 C 25.5 C 25.5 C initial temp of warm water 35.2 C 40.9 C 37.1 C final temp of water in calorimeter 32.5 C 32.9 C 30.9 C Enthalpy of Neutralization Trial 1 trial 2 trial 3 volume of 2.0 M HCl...
The Heat Capacity of Metals Data Calorimeter Constant Determination: Mass of cups and cool water(g) 27.15...
The Heat Capacity of Metals Data Calorimeter Constant Determination: Mass of cups and cool water(g) 27.15 Mass of cups and cool water(g) 56.12 Mass of cups, cool water, and hot water(g) 93.62 Initial temperature of cool water and calorimeter (c) 21.9 Initial temperature of hot water (c) 94.0 Final temperature of hot water, cool water, and calorimeter (c) 53.0 Calculate the calorimeter constant from your data. 1. How much heat (in Joules) is required to raise the temperature of 50...
A glass plate has a mass of 0.50 kg and a specific heat capacity of 840...
A glass plate has a mass of 0.50 kg and a specific heat capacity of 840 J/(kg·C°). The wavelength of infrared light is 6 × 10-5 m, while the wavelength of blue light is 4.7 × 10-7 m. Find the number of infrared photons and the number of blue photons needed to raise the temperature of the glass plate by 2.0 °C, assuming that all the photons are absorbed by the glass.
Indeed! So to summarize, planning involves laying down a path to the desired goal/s, and control...
Indeed! So to summarize, planning involves laying down a path to the desired goal/s, and control involves periodically monitoring activities and outcomes to measure progress towards the accomplishment of those goal/s. For example, similar to what some of you mentioned, the accountant provides historical information to help make the budget (plan) for the upcoming period, and also reports on the results of the performance for the current period so that management (or administration) knows if adjustments should be made to...
At what rate must heat be supplied to 15.0 kg/s of air, if the temperature is...
At what rate must heat be supplied to 15.0 kg/s of air, if the temperature is increased from 61.0°C to 650°C? a) Calculate the rate that heat must be supplied by integrating the heat capacity formula for air. b) Calculate the rate that heat must be supplied using the specific enthalpy table of gases located in your text by following the steps below. What is the specific enthalpy of air at 61.0°C, if the reference state is pref = 1...
What product(s) forms at the anode in the electrolysis of an aqueous solution of Na3PO4? What...
What product(s) forms at the anode in the electrolysis of an aqueous solution of Na3PO4? What product(s) forms at the anode in the electrolysis of an aqueous solution of FeI2? How do you solve both of these and what is the difference between them?
A car’s radiator is a heat exchanger with 2 kg/s of hot water entering at 100...
A car’s radiator is a heat exchanger with 2 kg/s of hot water entering at 100 C and leaving at 60 C with a pressure of 200 kPa. Air flows across the heat exchanger entering at 25 C and leaving at 40 C. What is the volume flowrate of air needed in m3/s? (18.9 m3/s)
Buffer capacity is a measure of a buffer solution\'s resistance to changes in pH as strong...
Buffer capacity is a measure of a buffer solution\'s resistance to changes in pH as strong acid or base is added. Suppose that you have 135 mL of a buffer that is 0.400 M in both acetic acid (CH3COOH) and its conjugate base (CH3COO–). Calculate the maximum volume of 0.340 M HCl that can be added to the buffer before its buffering capacity is lost.
Buffer capacity is a measure of a buffer solution\'s resistance to changes in pH as strong...
Buffer capacity is a measure of a buffer solution\'s resistance to changes in pH as strong acid or base is added. Suppose that you have 125 mL of a buffer that is 0.400 M in both propanoic acid (C2H5COOH) and its conjugate base (C2H5COO–). Calculate the maximum volume of 0.290 M HCl that can be added to the buffer before its buffering capacity is lost.
Buffer capacity is a measure of a buffer solution\'s resistance to changes in pH as strong...
Buffer capacity is a measure of a buffer solution\'s resistance to changes in pH as strong acid or base is added. Suppose that you have 175 mL of a buffer that is 0.240 M in both formic acid (HCOOH) and its conjugate base (HCOO–). Calculate the maximum volume of 0.380 M HCl that can be added to the buffer before its buffering capacity is lost.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT